that's easy to answer!

>From NFPA 13 (most editions for years):

 

5.2* Light Hazard Occupancies. Light hazard occupancies shall

be defined as occupancies or portions of other occupancies

where the quantity and/or combustibility of contents is low and

fires with relatively low rates of heat release are expected.

5.3* Ordinary Hazard Occupancies.

5.3.1* Ordinary Hazard (Group 1).

5.3.1.1 Ordinary hazard (Group 1) occupancies shall be defined

as occupancies or portions of other occupancies where

combustibility is low, quantity of combustibles is moderate,

stockpiles of combustibles do not exceed 8 ft (2.4 m), and fires

with moderate rates of heat release are expected.

5.3.1.2 Dedicated and miscellaneous storage shall be protected

in accordance with Chapter 12 and Chapter 13 as applicable.

5.3.2* Ordinary Hazard (Group 2).

5.3.2.1 Ordinary hazard (Group 2) occupancies shall be defined

as occupancies or portions of other occupancies where the

quantity and combustibility of contents are moderate to high,

stockpiles of contents with moderate rates of heat release do not

exceed 12 ft (3.66 m), and stockpiles of contents with high rates

of heat release do not exceed 8 ft (2.4 m).

5.3.2.2 Dedicated and miscellaneous storage shall be protected

in accordance with Chapter 12 and Chapter 13 as applicable.

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, December 05, 2016 9:36 AM
To: sprinklerforum
Subject: College Lab Classrooms

 

Quick question.

College Lab classrooms.  Light or Ordinary hazard?

 

Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786
fax 941-391-6133
[email protected]
www.wfmconsultinginc.com

 