Sorry, but that comment is so disconnected from the topic of this thread that 
it's just inappropriate. What happened in Oakland was criminal negligence, and 
has nothing to do with occupancy classification of academic laboratories. 
Please try to give some thought to your comments.


Steve


-------- Original message --------
From: Brad Casterline <[email protected]>
Date: 12/5/16 4:38 PM (GMT-08:00)
To: [email protected]
Subject: Re: College Lab Classrooms


And why stop at LABS?
How about ART ROOMS?
as the recent horrific and disgusting  tragedy in Oakland reveals.
If it's Contents that determine  LH vs OH, what about the glues and paints and 
paper mache and fabrics and all the other organic materials piled up and strewn 
about?

Brad

On Dec 5, 2016 6:05 PM, "Brad Casterline" 
<[email protected]<mailto:[email protected]>> wrote:

Sorry Bill I couldn't help it- it's more like I harp on this- but not as often
anymore, and thanks to Larry I'm sure I'm not the only one whom cracked open 
NFPA 45 for the first time today and found some numbers relating to common 13 
hazard classifications.

Hey Larry, when are you guys going to stop adding stuff to 13 (2016)?

Regards,
Surely

On Dec 5, 2016 9:54 AM, <[email protected]<mailto:[email protected]>> 
wrote:
Surely you jest.

________________________________
From: "Brad Casterline" 
<[email protected]<mailto:[email protected]>>
To: "sprinklerforum" 
<[email protected]<mailto:[email protected]>>
Sent: Monday, December 5, 2016 10:47:57 AM
Subject: RE: College Lab Classrooms

that's easy to answer!
>From NFPA 13 (most editions for years):

5.2* Light Hazard Occupancies. Light hazard occupancies shall
be defined as occupancies or portions of other occupancies
where the quantity and/or combustibility of contents is low and
fires with relatively low rates of heat release are expected.
5.3* Ordinary Hazard Occupancies.
5.3.1* Ordinary Hazard (Group 1).
5.3.1.1 Ordinary hazard (Group 1) occupancies shall be defined
as occupancies or portions of other occupancies where
combustibility is low, quantity of combustibles is moderate,
stockpiles of combustibles do not exceed 8 ft (2.4 m), and fires
with moderate rates of heat release are expected.
5.3.1.2 Dedicated and miscellaneous storage shall be protected
in accordance with Chapter 12 and Chapter 13 as applicable.
5.3.2* Ordinary Hazard (Group 2).
5.3.2.1 Ordinary hazard (Group 2) occupancies shall be defined
as occupancies or portions of other occupancies where the
quantity and combustibility of contents are moderate to high,
stockpiles of contents with moderate rates of heat release do not
exceed 12 ft (3.66 m), and stockpiles of contents with high rates
of heat release do not exceed 8 ft (2.4 m).
5.3.2.2 Dedicated and miscellaneous storage shall be protected
in accordance with Chapter 12 and Chapter 13 as applicable.

________________________________
From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of [email protected]<mailto:[email protected]>
Sent: Monday, December 05, 2016 9:36 AM
To: sprinklerforum
Subject: College Lab Classrooms

Quick question.
College Lab classrooms.  Light or Ordinary hazard?


Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786<tel:(941)%20421-9786>
fax 941-391-6133<tel:(941)%20391-6133>
[email protected]<mailto:[email protected]>
www.wfmconsultinginc.com<http://www.wfmconsultinginc.com>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to