FYI Oakland was an unsprinklered structure…….

Sadly 36+ lives were lost in modern America in a dry old warehouse used for an 
unintended purpose.

We all need to remind loved ones especially during the holiday season with 
large gatherings to be aware of their surroundings.

 

Jeff Bridges

JBFP Inc

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Monday, December 05, 2016 4:38 PM
To: [email protected]
Subject: Re: College Lab Classrooms

 

And why stop at LABS?
How about ART ROOMS?
as the recent horrific and disgusting  tragedy in Oakland reveals.
If it's Contents that determine  LH vs OH, what about the glues and paints and 
paper mache and fabrics and all the other organic materials piled up and strewn 
about?

Brad

On Dec 5, 2016 6:05 PM, "Brad Casterline" <[email protected] 
<mailto:[email protected]> > wrote:

Sorry Bill I couldn't help it- it's more like I harp on this- but not as often
anymore, and thanks to Larry I'm sure I'm not the only one whom cracked open 
NFPA 45 for the first time today and found some numbers relating to common 13 
hazard classifications.

Hey Larry, when are you guys going to stop adding stuff to 13 (2016)?

Regards, 
Surely

On Dec 5, 2016 9:54 AM, <[email protected] <mailto:[email protected]> > 
wrote:

Surely you jest.

 


  _____  


From: "Brad Casterline" <[email protected] 
<mailto:[email protected]> >
To: "sprinklerforum" <[email protected] 
<mailto:[email protected]> >
Sent: Monday, December 5, 2016 10:47:57 AM
Subject: RE: College Lab Classrooms

 

that's easy to answer!

>From NFPA 13 (most editions for years):

 

5.2* Light Hazard Occupancies. Light hazard occupancies shall

be defined as occupancies or portions of other occupancies

where the quantity and/or combustibility of contents is low and

fires with relatively low rates of heat release are expected.

5.3* Ordinary Hazard Occupancies.

5.3.1* Ordinary Hazard (Group 1).

5.3.1.1 Ordinary hazard (Group 1) occupancies shall be defined

as occupancies or portions of other occupancies where

combustibility is low, quantity of combustibles is moderate,

stockpiles of combustibles do not exceed 8 ft (2.4 m), and fires

with moderate rates of heat release are expected.

5.3.1.2 Dedicated and miscellaneous storage shall be protected

in accordance with Chapter 12 and Chapter 13 as applicable.

5.3.2* Ordinary Hazard (Group 2).

5.3.2.1 Ordinary hazard (Group 2) occupancies shall be defined

as occupancies or portions of other occupancies where the

quantity and combustibility of contents are moderate to high,

stockpiles of contents with moderate rates of heat release do not

exceed 12 ft (3.66 m), and stockpiles of contents with high rates

of heat release do not exceed 8 ft (2.4 m).

5.3.2.2 Dedicated and miscellaneous storage shall be protected

in accordance with Chapter 12 and Chapter 13 as applicable.

 


  _____  


From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of 
[email protected] <mailto:[email protected]> 
Sent: Monday, December 05, 2016 9:36 AM
To: sprinklerforum
Subject: College Lab Classrooms

 

Quick question.

College Lab classrooms.  Light or Ordinary hazard?

 

Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786 <tel:(941)%20421-9786> 
fax 941-391-6133 <tel:(941)%20391-6133> 
[email protected] <mailto:[email protected]> 
www.wfmconsultinginc.com <http://www.wfmconsultinginc.com> 

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to