Surely you jest. 

----- Original Message -----

From: "Brad Casterline" <[email protected]> 
To: "sprinklerforum" <[email protected]> 
Sent: Monday, December 5, 2016 10:47:57 AM 
Subject: RE: College Lab Classrooms 



that's easy to answer! 

>From NFPA 13 (most editions for years): 

  

5.2* Light Hazard Occupancies. Light hazard occupancies shall 

be defined as occupancies or portions of other occupancies 

where the quantity and/or combustibility of contents is low and 

fires with relatively low rates of heat release are expected. 

5.3* Ordinary Hazard Occupancies. 

5.3.1* Ordinary Hazard (Group 1). 

5.3.1.1 Ordinary hazard (Group 1) occupancies shall be defined 

as occupancies or portions of other occupancies where 

combustibility is low, quantity of combustibles is moderate, 

stockpiles of combustibles do not exceed 8 ft (2.4 m), and fires 

with moderate rates of heat release are expected. 

5.3.1.2 Dedicated and miscellaneous storage shall be protected 

in accordance with Chapter 12 and Chapter 13 as applicable. 

5.3.2* Ordinary Hazard (Group 2). 

5.3.2.1 Ordinary hazard (Group 2) occupancies shall be defined 

as occupancies or portions of other occupancies where the 

quantity and combustibility of contents are moderate to high, 

stockpiles of contents with moderate rates of heat release do not 

exceed 12 ft (3.66 m), and stockpiles of contents with high rates 

of heat release do not exceed 8 ft (2.4 m). 

5.3.2.2 Dedicated and miscellaneous storage shall be protected 

in accordance with Chapter 12 and Chapter 13 as applicable. 

  



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected] 
Sent: Monday, December 05, 2016 9:36 AM 
To: sprinklerforum 
Subject: College Lab Classrooms 


  


Quick question. 


College Lab classrooms.  Light or Ordinary hazard? 


  


Bill Menster 
WFM Consulting Inc. 
2416 Malaya Ct. 
Punta Gorda, FL 33983 
ph. 941-421-9786 
fax 941-391-6133 
[email protected] 
www.wfmconsultinginc.com 

  

_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 


_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to