You did not say you could not raise the 3” pipe.  Couldn’t you raise it and put 
pendants in?  Since the piping is obviously exposed, is there any reason you 
can’t comply with deflector-to-deck distances if you do that?  If the pendants 
extending below the piping is a height or exposure-to-mechanical-damage issue, 
install a listed headguard on it.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
[email protected]  \  burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
*Registered in: MN, PA, & TX
**NICET IV - Water-Based Systems Layout

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Friday, January 13, 2017 5:25 PM
To: [email protected]
Subject: Uprights on 3" pipe

In a light or ordinary hazard area, would you be able to justify uprights 
directly on a 3" main?

I have been hired to do the 3D coordination of a project designed by a 
consultant. The consultant indicated uprights directly on the 3" main.

I can justify it in that the main is non-structural and this is a light hazard 
area. However, there is also the section that states you can not put uprights 
on pipe 3" and larger without a sprig or arm over that would comply with the 3x 
rule.

There is no room to lower the pipe and I am semi-restricted from lateral 
movement for various other reasons.

What does the collective wisdom think with this scenario? And I don't need 
formulae with a hundred exponents and variables to figure this out.

Have a great weekend. Thanks in advance.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to