Beam depth keeps me from going up. Already using obstructed beam rules. 18" 
beams. If pipe tight to beam then bottom of pipe is 21.5" and a pendent would 
be about 24" below deck. 

I think they need sprigs or arm overs. But before I raise issues about this I 
wanted to be sure others thought it had to have sprigs or arm over as well. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 13, 2017, at 4:41 PM, Hinson, Ryan <[email protected]> wrote:
> 
> You did not say you could not raise the 3” pipe.  Couldn’t you raise it and 
> put pendants in?  Since the piping is obviously exposed, is there any reason 
> you can’t comply with deflector-to-deck distances if you do that?  If the 
> pendants extending below the piping is a height or 
> exposure-to-mechanical-damage issue, install a listed headguard on it.
>  
> Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
> Senior Fire Protection Engineer
> O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
> [email protected]  \  burnsmcd.com
> 8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
> *Registered in: MN, PA, & TX
> **NICET IV - Water-Based Systems Layout
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Friday, January 13, 2017 5:25 PM
> To: [email protected]
> Subject: Uprights on 3" pipe
>  
> In a light or ordinary hazard area, would you be able to justify uprights 
> directly on a 3" main?
>  
> I have been hired to do the 3D coordination of a project designed by a 
> consultant. The consultant indicated uprights directly on the 3" main. 
>  
> I can justify it in that the main is non-structural and this is a light 
> hazard area. However, there is also the section that states you can not put 
> uprights on pipe 3" and larger without a sprig or arm over that would comply 
> with the 3x  rule. 
>  
> There is no room to lower the pipe and I am semi-restricted from lateral 
> movement for various other reasons. 
>  
> What does the collective wisdom think with this scenario? And I don't need 
> formulae with a hundred exponents and variables to figure this out. 
>  
> Have a great weekend. Thanks in advance. 
>  
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to