I agree, I’m just trying to find where it was allowed in earlier editions.
[cid:[email protected]] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Friday, January 27, 2017 1:59 PM To: [email protected] Subject: Re: Tank Capacity You are just using a "break tank" when you have automatic refill. If your demand is 1000 gpm for 60 min and your city supply can do 500 gpm, then you just store 500 gpm for 60 min. I'm out on the road so I can't look up the exact reference. But the good thing is you don't need crazy formulae with a hundred exponents to figure this out. It's just simple math. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Jan 27, 2017, at 12:52 PM, Dale Wingard <[email protected]<mailto:[email protected]>> wrote: NFPA 22 (2013 Edition) excerpt- 4.1.4 A tank shall be sized so that the stored supply plus reliable automatic refill shall be sufficient to meet the demand placed upon it for the design duration. I have researched earlier editions but I have not been able to find where the reliable automatic refill has been previously allowed; however, I recall this being the case. Am I overlooking something? Thanks, <image001.jpg> <Dale Wingard SET.vcf> _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org