The tank and pumps will be supplying the yard loop with the fire hydrants.  It 
is required to be included.



[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, January 27, 2017 4:08 PM
To: [email protected]
Subject: RE: Tank Capacity

Hose demand is usually not art of the equation with good city hydrant supply 
available.
If you omit hose than it all works.

Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dale Wingard
Sent: Friday, January 27, 2017 4:37 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Tank Capacity

Thanks everyone.  I just thought that it was always an acceptable practice.

The situation is I have a new owner of a warehouse with an existing ground tank 
and pump house.  We will be replacing the pump.  The tank is only 3000 gallons 
short of the largest system demand plus the outside hose times the duration 
requirement.  The city supply to the tank will be more than able to make up the 
difference.  The underwriter is saying that the “reliable automatic refill” 
cannot be considered.

I was wanting to show proof that it was acceptable prior to the 2013 edition.



[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Friday, January 27, 2017 3:22 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Tank Capacity

It was in one edition of 13R wayback when. I don't think it had ever been 
"allowed" by 22 until recently but it only makes sense. Now define reliable 
refill rate for this application emphasizing reliable.
On Fri, Jan 27, 2017 at 12:48 PM Brad Casterline 
<[email protected]<mailto:[email protected]>> wrote:

Requirements for break tanks were added NFPA 20 (2007), according to page 20-2.

Brad
On Jan 27, 2017 2:41 PM, "Mike B Morey" 
<[email protected]<mailto:[email protected]>> wrote:
The earliest reference I can find is NFPA 25 2007 in section 5.30, it has moved 
around since, but as others have pointed out, it's defined in there as a break 
tank.
________________________________

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824<tel:(260)%20487-7824> /  cell 
260.417.0625<tel:(260)%20417-0625> /  fax 260.487.7991<tel:(260)%20487-7991>
email [email protected]<mailto:[email protected]>

[cid:[email protected]]





From:        Dale Wingard <[email protected]<mailto:[email protected]>>
To:        
"[email protected]<mailto:[email protected]>"
 
<[email protected]<mailto:[email protected]>>
Date:        01/27/2017 02:52 PM
Subject:        Tank Capacity
Sent by:        "Sprinklerforum" 
<[email protected]<mailto:[email protected]>>
________________________________



NFPA 22 (2013 Edition) excerpt-

4.1.4 A tank shall be sized so that the stored supply plus reliable automatic 
refill shall be sufficient to meet the demand placed upon it for the design 
duration.

I have researched earlier editions but I have not been able to find where the 
reliable automatic refill has been previously allowed; however, I recall this 
being the case.  Am I overlooking something?

Thanks,


[cid:[email protected]]
 [attachment "Dale Wingard  SET.vcf" deleted by Mike B 
Morey/Shambaugh/EMCORGROUP] _______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=ZIlAYkYGG--WYErIebjpFDdfGghXLB-667jMo2EgODU&s=qOSLfkv2O4_vGbMHmTDjJ1Ouas46DTZW6qD5O1rpvcc&e=
This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile

________________________________
[Avast 
logo]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


This email has been checked for viruses by Avast antivirus software.
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


<<attachment: Dale Wingard SET2.vcf>>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to