The earliest reference I can find is NFPA 25 2007 in section 5.30, it has 
moved around since, but as others have pointed out, it's defined in there 
as a break tank. 



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   Dale Wingard <[email protected]>
To:     "[email protected]" 
<[email protected]>
Date:   01/27/2017 02:52 PM
Subject:        Tank Capacity
Sent by:        "Sprinklerforum" 
<[email protected]>



NFPA 22 (2013 Edition) excerpt- 
 
4.1.4 A tank shall be sized so that the stored supply plus reliable 
automatic refill shall be sufficient to meet the demand placed upon it for 
the design duration.
 
I have researched earlier editions but I have not been able to find where 
the reliable automatic refill has been previously allowed; however, I 
recall this being the case.  Am I overlooking something? 
 
Thanks,
 
 

 [attachment "Dale Wingard  SET.vcf" deleted by Mike B 
Morey/Shambaugh/EMCORGROUP] 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=ZIlAYkYGG--WYErIebjpFDdfGghXLB-667jMo2EgODU&s=qOSLfkv2O4_vGbMHmTDjJ1Ouas46DTZW6qD5O1rpvcc&e=
 




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to