A 1000 GPM rated pump will not likely produce a flow rate of 1800 GPM. It will 
limit out most likely around 1650 to maybe 1700 GPM. It should then, 
nonetheless provide the minimum design density at the lest demanding design 
area. There is no code requirement to produce the maximum flow capacity of a 
design area, only the minimum.
Mark at Aero
602 820-7894

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reza Esmaeili
Sent: Monday, January 30, 2017 1:56 PM
To: [email protected]
Subject: Selecting a Fire Pump/ Europeans vs. Americans

 I am glad to write in this nice forum again!

I don’t understand NFPA 20 for selecting fire pump: “Maximum system demand flow 
should be between 90% and 140% of pump’s rated capacity, but, in no case, 
greater than 150% of the pump’s rated capacity”.

That is to say if my total sprinkler and hose demand is 1400GPM, I can simply 
choose a 1000GPM rated pump. 1400GPM is calculated based on the most remote 
sprinklers, so what if the sprinklers nearer to pumps are activated and my 
demand jump to 1800GPM? Then at high flow, there is a possibility for 
cavitation and overloading the motor. Am I wrong?

Europeans calculate differently. They calculate the demand both at the most 
unfavourable area (most remote area) and most favourable area (near the pump). 
For example if they calculate 1400GPM at most unfavourable and 1800GPM at most 
favourable area, then based on these figures they choose a pump. They also 
check 1800GPM on the pump curve to be sure it’s less than 140% of rated 
capacity and also less than 16m NPSHr.

VdS CEA 4001 Standard in Europe: The pump set shall be capable of providing at 
least the flow and pressure of both the most favourable and the most 
unfavourable areas. The maximum flow demand (Qmax) for supplying the most 
favourable area may exceed the permitted rate by up to 40 %. The pressure shall 
not fall by more than 30 % (of the pressure prevailing with the permitted 
rate). The flow demand for the most unfavourable area shall fall below the 
permitted rate at all times.

NFPA 20 and VdS are somehow the same. They limit the maximum flow demand up to 
140% of rated capacity, but Europeans really calculate the minimum and maximum 
demand and check this is less than 140% but American don’t check anything. So 
if like the above example an American designer make a tight selection (Choosing 
a 1000GPM pump for 1400GPM demand), is there any possible problem if the 
sprinklers near the pumps are activated and the pump runs at 1800GPM?

Best,

Reza Esmaeili

Email:[email protected]
Cell: +98 912 2444875
Web: www.sarian.ir
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to