Isn't the requirement for calculating the area closest to the pump only
when the water supply is water storage tank, to verify the tank capacity
against flow rate and duration?
You are right though - American codes do not require the two sets-- we calc
'most remote' and use that size all the way back because the closer you get
to the riser the more you will be flowing, hence the concern about tank
capacity.
It is a can of worms that has not yet been opened here in 'the states'.

Brad
A 1000 GPM rated pump will not likely produce a flow rate of 1800 GPM. It
will limit out most likely around 1650 to maybe 1700 GPM. It should then,
nonetheless provide the minimum design density at the lest demanding design
area. There is no code requirement to produce the maximum flow capacity of
a design area, only the minimum.
Mark at Aero
602 820-7894

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Reza Esmaeili
Sent: Monday, January 30, 2017 1:56 PM
To: [email protected]
Subject: Selecting a Fire Pump/ Europeans vs. Americans

 I am glad to write in this nice forum again!

I don’t understand NFPA 20 for selecting fire pump: “Maximum system demand
flow should be between 90% and 140% of pump’s rated capacity, but, in no
case, greater than 150% of the pump’s rated capacity”.

That is to say if my total sprinkler and hose demand is 1400GPM, I can
simply choose a 1000GPM rated pump. 1400GPM is calculated based on the most
remote sprinklers, so what if the sprinklers nearer to pumps are activated
and my demand jump to 1800GPM? Then at high flow, there is a possibility
for cavitation and overloading the motor. Am I wrong?

Europeans calculate differently. They calculate the demand both at the most
unfavourable area (most remote area) and most favourable area (near the
pump). For example if they calculate 1400GPM at most unfavourable and
1800GPM at most favourable area, then based on these figures they choose a
pump. They also check 1800GPM on the pump curve to be sure it’s less than
140% of rated capacity and also less than 16m NPSHr.

VdS CEA 4001 Standard in Europe: The pump set shall be capable of providing
at least the flow and pressure of both the most favourable and the most
unfavourable areas. The maximum flow demand (Qmax) for supplying the most
favourable area may exceed the permitted rate by up to 40 %. The pressure
shall not fall by more than 30 % (of the pressure prevailing with the
permitted rate). The flow demand for the most unfavourable area shall fall
below the permitted rate at all times.

NFPA 20 and VdS are somehow the same. They limit the maximum flow demand up
to 140% of rated capacity, but Europeans really calculate the minimum and
maximum demand and check this is less than 140% but American don’t check
anything. So if like the above example an American designer make a tight
selection (Choosing a 1000GPM pump for 1400GPM demand), is there any
possible problem if the sprinklers near the pumps are activated and the
pump runs at 1800GPM?

Best,

Reza Esmaeili

Email:[email protected]
Cell: +98 912 2444875
Web: www.sarian.ir
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to