Sure Reza, wish I could have helped. My knowledge of the European Code is
limited to the interesting differences Europeans vs. Americans via the
Excellent summary Damien Shannon provided me off Forum a few years ago. I
love both!, and one of the things that stuck out was the 'two calc'
regarding tank capacity.
I know Chris Cahill (American Forumite) is aware of it :)

Brad
.
On Jan 30, 2017 4:12 PM, "Reza Esmaeili" <[email protected]> wrote:

> Brad,
> Thanks for your comment. It's not about water tank storage. It's about
> considering the maximum flow at the area closet to the pump just in order
> to select the right pump. Check this figure in VdS CEA 4001 Standard:
>
> http://www.sarian.ir/Pump-Curve.png
>
>  Best,
>  Reza Esmaeili
>
>  Email:[email protected]
>  Cell: +98 912 2444875
>  Web: www.sarian.ir
>
> --------------------------------------------
> On Tue, 1/31/17, Brad Casterline <[email protected]> wrote:
>
>  Subject: RE: Selecting a Fire Pump/ Europeans vs. Americans
>  To: [email protected]
>  Date: Tuesday, January 31, 2017, 1:03 AM
>
>  Isn't
>  the requirement for calculating the area closest to the pump
>  only when the water supply is water storage tank, to verify
>  the tank capacity against flow rate and duration?
>
>  You are right though - American codes do not require the two
>  sets-- we calc 'most remote' and use that size all
>  the way back because the closer you get to the riser the
>  more you will be flowing, hence the concern about tank
>  capacity.
>
>  It is a can of worms that has not yet been opened here in
>  'the states'.
>  Brad
>  A 1000
>  GPM rated pump will not likely produce a flow rate of 1800
>  GPM. It will limit out most likely around 1650 to maybe 1700
>  GPM. It should then, nonetheless provide the minimum design
>  density at the lest demanding design area. There is no code
>  requirement to produce the maximum flow capacity of a design
>  area, only the minimum.
>
>  Mark at Aero
>
>  602 820-7894
>
>
>
>  -----Original Message-----
>
>  From: Sprinklerforum [mailto:sprinklerforum-
>  [email protected]. org] On Behalf Of Reza
>  Esmaeili
>
>  Sent: Monday, January 30, 2017 1:56 PM
>
>  To: sprinklerforum@lists.
>  firesprinkler.org
>
>  Subject: Selecting a Fire Pump/ Europeans vs. Americans
>
>
>
>   I am glad to write in this nice forum again!
>
>
>
>  I don’t understand NFPA 20 for selecting fire pump:
>  “Maximum system demand flow should be between 90% and 140%
>  of pump’s rated capacity, but, in no case, greater than
>  150% of the pump’s rated capacity”.
>
>
>
>  That is to say if my total sprinkler and hose demand is
>  1400GPM, I can simply choose a 1000GPM rated pump. 1400GPM
>  is calculated based on the most remote sprinklers, so what
>  if the sprinklers nearer to pumps are activated and my
>  demand jump to 1800GPM? Then at high flow, there is a
>  possibility for cavitation and overloading the motor. Am I
>  wrong?
>
>
>
>  Europeans calculate differently. They calculate the demand
>  both at the most unfavourable area (most remote area) and
>  most favourable area (near the pump). For example if they
>  calculate 1400GPM at most unfavourable and 1800GPM at most
>  favourable area, then based on these figures they choose a
>  pump. They also check 1800GPM on the pump curve to be sure
>  it’s less than 140% of rated capacity and also less than
>  16m NPSHr.
>
>
>
>  VdS CEA 4001 Standard in Europe: The pump set shall be
>  capable of providing at least the flow and pressure of both
>  the most favourable and the most unfavourable areas. The
>  maximum flow demand (Qmax) for supplying the most favourable
>  area may exceed the permitted rate by up to 40 %. The
>  pressure shall not fall by more than 30 % (of the pressure
>  prevailing with the permitted rate). The flow demand for the
>  most unfavourable area shall fall below the permitted rate
>  at all times.
>
>
>
>  NFPA 20 and VdS are somehow the same. They limit the maximum
>  flow demand up to 140% of rated capacity, but Europeans
>  really calculate the minimum and maximum demand and check
>  this is less than 140% but American don’t check anything.
>  So if like the above example an American designer make a
>  tight selection (Choosing a 1000GPM pump for 1400GPM
>  demand), is there any possible problem if the sprinklers
>  near the pumps are activated and the pump runs at
>  1800GPM?
>
>
>
>  Best,
>
>
>
>  Reza Esmaeili
>
>
>
>  Email:[email protected]
>
>  Cell: +98 912 2444875
>
>  Web: www.sarian.ir
>
>  ______________________________ _________________
>
>  Sprinklerforum mailing list
>
>  Sprinklerforum@lists.
>  firesprinkler.org
>
>  http://lists.firesprinkler.
>  org/listinfo.cgi/ sprinklerforum-firesprinkler. org
>
>  ______________________________ _________________
>
>  Sprinklerforum mailing list
>
>  Sprinklerforum@lists.
>  firesprinkler.org
>
>  http://lists.firesprinkler.
>  org/listinfo.cgi/ sprinklerforum-firesprinkler. org
>
>
>  -----Inline Attachment Follows-----
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to