Hello Todd,

 

The original building plans are not available.  I am considering this to be a 
Class II metal deck roof, and assuming tar and gravel, foam insulation, a 
combustible vapor barrier, and combustible adhesive over a steel deck.

 

David 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, March 10, 2017 5:00 PM
To: Sprinklerforum
Subject: Re: Built-up roof deck as a limited-combustible construction

 

Any more details on what the built up roof consists of?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)






On Mar 10, 2017 at 4:57 PM, <David Bitton <mailto:[email protected]> 
> wrote:

Hello,

 

I have a 35 ft high building being built adjacent to a 22 ft high building 
which has a built-up, insulated metal deck roof. The structural engineer has 
devised a sloped "snow shed" between the addition and the lower building in 
order to distribute the increased snow load at this juncture.  This will create 
an inaccessible concealed space on the roof which will be of noncombustible 
construction, with the exception of its base, which will be the built-up metal 
deck roof of the existing building.  Would you consider this as meeting the 
definition of "limited combustible construction", meaning that the space would 
not require sprinkler protection?

 

David Bitton, ing./Eng.


Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, Québec 

H4P 1T8

 

T: (514) 341-4545     C: (514) 996-7483

www.questlosscontrol.com

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to