I agree with Todd.  The standard says, “Concealed spaces of exposed combustible 
construction shall be protected …”

This trumps the subjective hair splitting with regard to what constitutes 
limited combustible construction and to what extent combustible material might 
be allowed in limited amounts.  You have one entire and continuous surface that 
encapsulates the concealed space(s) in question; that’s not limited, IMHO.

Steve L.



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, March 10, 2017 4:07 PM
To: Sprinklerforum
Subject: Re: RE: Built-up roof deck as a limited-combustible construction

I think the term Limited Combustible is purposely vague. Personally, I would 
think this is not limited since it covers the entire flat space and there is 
continuity. If a fire did get into that space, it could run over the entire 
structure with no good way for the fire department to fight it.

What a local authority or insurance company would say is something else. You 
probably should consult with them.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)



On Mar 10, 2017 at 5:47 PM, <David Bitton<mailto:[email protected]>> 
wrote:
Yes, it is a flat roof, built in 1973.  I have no doubt that it will burn, and 
I am classifying it as a combustible roof.  (I know about the fire at the GM 
plant in Livonia.)  My question is more along the line of: Can a noncombustible 
structure built on top of a typical built-up roof deck with combustible 
insulation meet NFPA 13's definition of "Limited-combustible construction"?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, March 10, 2017 5:14 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Built-up roof deck as a limited-combustible construction

Is it a flat roof?
Is it covered with gravel or stone?
If it is built of felt paper and asphalt/tar it will burn.

Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of David Bitton
Sent: Friday, March 10, 2017 4:57 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Built-up roof deck as a limited-combustible construction

Hello,

I have a 35 ft high building being built adjacent to a 22 ft high building 
which has a built-up, insulated metal deck roof. The structural engineer has 
devised a sloped "snow shed" between the addition and the lower building in 
order to distribute the increased snow load at this juncture.  This will create 
an inaccessible concealed space on the roof which will be of noncombustible 
construction, with the exception of its base, which will be the built-up metal 
deck roof of the existing building.  Would you consider this as meeting the 
definition of "limited combustible construction", meaning that the space would 
not require sprinkler protection?

David Bitton, ing./Eng.
Quest Loss Control Services Inc.
5100, rue de la Savane, bureau 200
Montréal, Québec
H4P 1T8

T: (514) 341-4545     C: (514) 996-7483
www.questlosscontrol.com<../../../../Documents/Sara's%20Important%20Stuff/HR/www.questlosscontrol.com>



[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to