3.3.13 specifically defines Limited Combustible, I would not consider that “purposefully vague”. If the construction does not meet the definition or you cannot make that determination, I do not see a way to exclude sprinklers from this area.
Ryan Labrie Fire Protection Designer Critical System Solutions, LLC 2830 Scherer Drive, Suite 300 St. Petersburg, FL 33716 Office: 727.209.5122 Fax: 727.209.5126 Cell: 813.394.3978 Email: [email protected]<mailto:[email protected]> [cid:[email protected]] From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, March 10, 2017 7:07 PM To: Sprinklerforum Subject: Re: RE: Built-up roof deck as a limited-combustible construction I think the term Limited Combustible is purposely vague. Personally, I would think this is not limited since it covers the entire flat space and there is continuity. If a fire did get into that space, it could run over the entire structure with no good way for the fire department to fight it. What a local authority or insurance company would say is something else. You probably should consult with them. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080<tel:860-535-2080> (ofc) 860-553-3553<tel:860-553-3553> (fax) 860-608-4559<tel:860-608-4559> (cell) On Mar 10, 2017 at 5:47 PM, <David Bitton<mailto:[email protected]>> wrote: Yes, it is a flat roof, built in 1973. I have no doubt that it will burn, and I am classifying it as a combustible roof. (I know about the fire at the GM plant in Livonia.) My question is more along the line of: Can a noncombustible structure built on top of a typical built-up roof deck with combustible insulation meet NFPA 13's definition of "Limited-combustible construction"? From: Sprinklerforum [mailto:[email protected]] On Behalf Of Art Tiroly Sent: Friday, March 10, 2017 5:14 PM To: [email protected]<mailto:[email protected]> Subject: RE: Built-up roof deck as a limited-combustible construction Is it a flat roof? Is it covered with gravel or stone? If it is built of felt paper and asphalt/tar it will burn. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell From: Sprinklerforum [mailto:[email protected]] On Behalf Of David Bitton Sent: Friday, March 10, 2017 4:57 PM To: [email protected]<mailto:[email protected]> Subject: Built-up roof deck as a limited-combustible construction Hello, I have a 35 ft high building being built adjacent to a 22 ft high building which has a built-up, insulated metal deck roof. The structural engineer has devised a sloped "snow shed" between the addition and the lower building in order to distribute the increased snow load at this juncture. This will create an inaccessible concealed space on the roof which will be of noncombustible construction, with the exception of its base, which will be the built-up metal deck roof of the existing building. Would you consider this as meeting the definition of "limited combustible construction", meaning that the space would not require sprinkler protection? David Bitton, ing./Eng. Quest Loss Control Services Inc. 5100, rue de la Savane, bureau 200 Montréal, Québec H4P 1T8 T: (514) 341-4545 C: (514) 996-7483 www.questlosscontrol.com<../../../../Documents/Sara's%20Important%20Stuff/HR/www.questlosscontrol.com> [https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org