Mercantile (Group M) is how retail is classified in the building code.   For 
our purposes Retail = Mercantile = Store = Dispensary (In Colorado, Washington 
and select other states).

Obviously there are exceptions.  Stores with racks, tire stores, other higher 
combustible-loaded "retail" uses require more robust fire protection.   But if 
you are confused about reference to an occupancy as Mercantile, it is usually 
(and that's USUALLY with emphasis) an OH2.

My opinion only,
Steve L.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Thursday, April 6, 2017 11:05 AM
To: [email protected]
Subject: RE: Retail Building

Retail vs Mercantile?

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Retail Building


Something just came up here.



What would stop someone from saying that any retail store (Small Strip Mall, 
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which calls 
for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary Hazard Group 
II?


Greg Lindholm
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org