Steve,

I was thinking along the lines of Chapter 20 that has "Retail Stores" as
part of the Special Designs of Storage Protection.   I don't disagree with
what you said about mercantile only it seems that the .6/2000 criteria Greg
mentioned was in reference to the retail store that has high hazard storage
and that it would only be appropriate for such occupancies.  It would be
inappropriate to attempt covering all retail with this criteria.   Though
you would have had to read a lot into my comment to get all that.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Thursday, April 06, 2017 2:13 PM
To: [email protected]; [email protected]
Subject: RE: Retail Building

 

Mercantile (Group M) is how retail is classified in the building code.   For
our purposes Retail = Mercantile = Store = Dispensary (In Colorado,
Washington and select other states).

 

Obviously there are exceptions.  Stores with racks, tire stores, other
higher combustible-loaded "retail" uses require more robust fire protection.
But if you are confused about reference to an occupancy as Mercantile, it is
usually (and that's USUALLY with emphasis) an OH2.

 

My opinion only,

Steve L.

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Thursday, April 6, 2017 11:05 AM
To: [email protected]
Subject: RE: Retail Building

 

Retail vs Mercantile?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: [email protected]
Subject: Retail Building

 

Something just came up here. 

 

What would stop someone from saying that any retail store (Small Strip Mall,
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which
calls for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary
Hazard Group II?

 

Greg Lindholm 