20.3 is an alternative to the Chapter 16 and Chapter 17 requirements for
"Big Box" retail stores; likely as another way to avoid in-rack sprinklers.

 

The ".shall be permitted." in paragraph 20.3.1 is key.  The designer has the
option of using the provisions of 20.3.1 if they meet all 13 of the
following conditions.  It does not mean the designer is required to meet the
two separate design points of 20.3.1.  The designer still has the option of
designing the system as per Chapter 16 or Chapter 17.  

 

 

David L. Miller, P.E.

Engineered Fire Protection, LLC

11920 Richcroft Avenue

Baton Rouge, Louisiana  70814

225-273-5040

 

From: Gregory Lindholm [mailto:[email protected]] 
Sent: Friday, April 07, 2017 12:10 PM
To: [email protected]
Subject: RE: Retail Building

 

Maybe I explained it wrong.

 

In the past, all Retail was labeled Mercantile, Ordinary Hazard Group II,
unless they specifically had storage over 12' high. Pretty much all Grocery
Stores went in OH Group II.

 

Now, what is stopping an AHJ from calling a Strip Mall with 13' deck and 10'
ceilings,  "Retail Store", and requiring the design to be as per 20.3?

 

What am I missing?

 

Greg Lindholm 

 

  _____  

From: Sprinklerforum <[email protected]
<mailto:[email protected]> > on behalf of
[email protected]
<mailto:[email protected]>
<[email protected]
<mailto:[email protected]> >
Sent: Thursday, April 6, 2017 3:34 PM
To: [email protected]
<mailto:[email protected]> 
Subject: Sprinklerforum Digest, Vol 49, Issue 3 

 

Send Sprinklerforum mailing list submissions to
        [email protected]
<mailto:[email protected]> 

To subscribe or unsubscribe via the World Wide Web, visit
 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g> Sprinklerforum Info Page - American Fire Sprinkler Association

lists.firesprinkler.org

Your email address: Your name (optional): You may enter a privacy password
below. This provides only mild security, but should prevent others from
messing ...




or, via email, send a message with subject or body 'help' to
        [email protected]
<mailto:[email protected]> 

You can reach the person managing the list at
        [email protected]
<mailto:[email protected]> 

When replying, please edit your Subject line so it is more specific
than "Re: Contents of Sprinklerforum digest..."


Today's Topics:

   1. Re: NFPA 13 dry system - residential sprinklers (Travis Mack, SET)
   2. RE: NFPA 13 dry system - residential sprinklers (Foster, Ed)
   3. RE: NFPA 13 dry system - residential sprinklers (Ed Kramer)
   4. Retail Building (Gregory Lindholm)
   5. RE: Retail Building (Bob)
   6. RE: Retail Building (Fox, Duane T. (FireMarshal))
   7. RE: Retail Building (Steve Leyton)
   8. NFPA 20 4.7.7.2  (Colin Carew (Cambridge))
   9. RE: NFPA 20 4.7.7.2 (John Irwin)
  10. RE: NFPA 20 4.7.7.2  (Prahl, Craig/GVL)
  11. RE: NFPA 20 4.7.7.2  (Tom Duross)


----------------------------------------------------------------------

Message: 1
Date: Thu, 6 Apr 2017 08:58:55 -0700
From: "Travis Mack, SET" <[email protected] <mailto:[email protected]> >
To: [email protected]
<mailto:[email protected]> 
Subject: Re: NFPA 13 dry system - residential sprinklers
Message-ID: <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="windows-1252"; Format="flowed"

You mean I just can't pick and choose the standard edition I want to 
use? :-)  I guess I am guilty of not reading the full text of the 
message.  Great catch, my friend.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com 


 <http://www.mfpdesign.com/> MFP Design

www.mfpdesign.com <http://www.mfpdesign.com> 

MFP Design, LLC was started in 2001. MFP Design, LLC provides fire sprinkler
drawings for architects, engineers and fire sprinkler contractors in the
industry.



https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack 


 <https://www.linkedin.com/in/travismack> Travis Mack | LinkedIn

www.linkedin.com <http://www.linkedin.com> 

View Travis Mack's professional profile on LinkedIn. LinkedIn is the world's
largest business network, helping professionals like Travis Mack discover
inside ...




On 4/6/2017 9:01 AM, Parsley Consulting wrote:
> Remember friends that the text Travis quoted was _*added*_ in the 2010 
> edition of -13.  Dewayne's inquiry began with a note that his project 
> was governed by the 2007.  Still, the value for dry system water 
> delivery time of 15 seconds for residential occupancies was the first 
> item in Table 7.2.3.6.1.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/> *** 


 <http://www.parsleyconsulting.com/> Parsley Consulting - Founded 1985, by
Donald L. Parsley ...

www.parsleyconsulting.com <http://www.parsleyconsulting.com> 

Parsley Consulting designs and reviews residential and commercial fire
suppression and alarm systems plans, and provides consulting services to
authorities having ...



> On 04/06/2017 8:36 AM, Travis Mack, SET wrote:
>>
>> It can be R or I occupancy.  It doesn't matter.  It is the fact you 
>> are protecting a dwelling unit with a dry pipe system.
>>
>> 7.2.3.6.3 For dry pipe systems protecting dwelling unit portions of 
>> any occupancy, the sprinklers in the dwelling unit shall have a 
>> maximum water delivery time of 15 seconds to the
>> single most remote sprinkler.
>>
>> It seems like you have 15 seconds regardless.  Now, if you have a dry 
>> pipe valve on the first floor and I believe you said these were on 
>> the 5th floor, it seems quite unlikely you will get 15 seconds.  My 
>> suggestion is to find a way to supply these sprinklers in the 
>> dwelling units from a wet pipe system.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> http://www.mfpdesign.com 


 <http://www.mfpdesign.com/> MFP Design

www.mfpdesign.com <http://www.mfpdesign.com> 

MFP Design, LLC was started in 2001. MFP Design, LLC provides fire sprinkler
drawings for architects, engineers and fire sprinkler contractors in the
industry.



>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 


 <https://www.facebook.com/pages/MFP-Design-LLC/92218417692> Log In or Sign
Up to View

www.facebook.com <http://www.facebook.com> 

See posts, photos and more on Facebook.



>> Send large files to us via:https://www.hightail.com/u/MFPDesign  
>> LinkedIn:https://www.linkedin.com/in/travismack
>> On 4/6/2017 8:16 AM, Dewayne Martinez wrote:
>>>
>>> That was one of my concerns also. R-2 floor occupancy, calculating 
>>> it per light hazard but using residential heads.  If the R-2 
>>> occupancy is what would dictate the 15sec delivery time then it 
>>> wouldn?t matter what type of heads I used in the residential areas.
>>>
>>> *From:*Sprinklerforum 
>>> [mailto:[email protected] 
>>> <mailto:[email protected]>] *On Behalf 
>>> Of *Travis Mack
>>> *Sent:* Thursday, April 06, 2017 8:58 AM
>>> *To:* [email protected]
<mailto:[email protected]>  
>>> <mailto:[email protected]>
>>> *Subject:* Re: NFPA 13 dry system - residential sprinklers
>>>
>>> Double check delivery times. I think you need a 15 second delivery 
>>> time in residential areas.
>>>
>>> Travis Mack, SET
>>>
>>> MFP Design, LLC
>>>
>>> "Follow" us on Facebook: 
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>
>>> Send large files to MFP Design via:
>>>
>>> https://www.hightail.com/u/MFPDesign
>>>
>>> Sent from my iPhone
>>>
>>>
>>> On Apr 6, 2017, at 6:31 AM, Dewayne Martinez 
>>> <[email protected]
<mailto:[email protected]%20%0b> 
>>> <mailto:[email protected]>> wrote:
>>>
>>>     The dry portion below the attic was laid out at max 15x15
>>>     spacing with the
>>>     lines at 15ft above the floor.  The way the rooms layout there
>>>     are long
>>>     runs with 8ft ceilings so I was going to drop down once to feed
>>>     all these
>>>     rooms with one line but I still need to size it.  This reviewer
>>>     will still
>>>     make us calculate the residential build out portion. I can get
>>>     by with a
>>>     1 1/4" line calculating  4 heads.
>>>
>>>     -----Original Message-----
>>>     From: Mark Phillips [mailto:[email protected]]
>>>     Sent: Thursday, April 06, 2017 8:17 AM
>>>     To: [email protected]
<mailto:[email protected]> 
>>>     <mailto:[email protected]>
>>>     Cc: [email protected]
<mailto:[email protected]> 
>>>     <mailto:[email protected]>
>>>     Subject: Re: NFPA 13 dry system - residential sprinklers
>>>
>>>     If I'm understanding
>>>     The roof system is unchanged and your adding a lower supply to
>>>     be rooms.
>>>
>>>     Use standard qr heads and same pipe sizes
>>>
>>>     The roof is still most demanding
>>>
>>>     Sent from my Verizon 4G LTE Droid
>>>     On Apr 6, 2017 9:14 AM, Dewayne Martinez
>>>     <[email protected]
<mailto:[email protected]%0b> 
>>>     <mailto:[email protected]>>
>>>     wrote:
>>>     NFPA 13 (07ed)
>>>
>>>     I have an existing 5th floor shell space that is installed as a
>>>     light
>>>     hazard dry system that has pipe in the shell space and in the
>>>     attic.  They
>>>     are turning this floor into a dormitory (R-2).
>>>     1)Can I use listed residential heads on return bends and only
>>>     pick up 4
>>>     heads per 11.3.1.1 or will I need to pick up 1950SF? What if
>>>     there are
>>>     incidental areas such as a laundry room, ect. in the same areas
>>>     as the
>>>     dorm rooms?
>>>     2)What would be the required trip time be per Table 7.2.3.6.1?
>>>      15sec for
>>>     residential or 60sec for light hazard?
>>>
>>>     Thanks,
>>>     Dewayne Martinez
>>>     Fire Protection Design Manager
>>>
>>>     TOTAL Mechanical
>>>     Building Integrity
>>>     W234 N2830 Paul Rd.
>>>     Pewaukee, WI  53072
>>>     [email protected]
<mailto:[email protected]> 
>>>     <mailto:[email protected]
<mailto:[email protected]%3e%3cmailto:dmartinez@total-mechanica
l.com> ><mailto:[email protected]>
>>>     Ph:  262-522-7110
>>>     Cell: 414-406-5208
>>>     http://www.total-mechanical.com/
>>>
>>>     [cid:[email protected]]
>>>     [cid:[email protected]]
>>>     [cid:[email protected]]  [Top Workplaces 2015]
>>>
>>>     TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.
>>>     _______________________________________________
>>>     Sprinklerforum mailing list
>>>     [email protected]
<mailto:[email protected]> 
>>>     <mailto:[email protected]>
>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
<mailto:[email protected]> 
>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
<mailto:[email protected]> 
>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
<mailto:[email protected]> 
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/67c723ca/attachment-0001.htm>

------------------------------

Message: 2
Date: Thu, 6 Apr 2017 16:32:30 +0000
From: "Foster, Ed" <[email protected] <mailto:[email protected]> >
To: "[email protected]
<mailto:[email protected]> "
        <[email protected]
<mailto:[email protected]> >
Subject: RE: NFPA 13 dry system - residential sprinklers
Message-ID:
        <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="us-ascii"

I have appreciated the many opportunities to learn much from reading the
exchanges on this forum.
Today I am inclined to add this comment:
"They are turning this floor into a dormitory (R-2)". I believe that the
change of occupancy classification / use would dictate compliance with the
code/ standards that are current to the time of change, which if I
understand this thread is the present. The recommendation to install a wet
system seems most appropriate.
One man's opinion.

Ed Foster
Fire Marshal
Fire Prevention Bureau
Carpinteria-Summerland Fire District
(805) 566-2451
[cid:82df1ca92855c9c2623baa3ddf8c0acda8677ac1@zimbra]

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Parsley Consulting
Sent: Thursday, April 06, 2017 9:02 AM
To: [email protected]
<mailto:[email protected]> 
Subject: Re: NFPA 13 dry system - residential sprinklers

Remember friends that the text Travis quoted was added in the 2010 edition
of -13.  Dewayne's inquiry began with a note that his project was governed
by the 2007.  Still, the value for dry system water delivery time of 15
seconds for residential occupancies was the first item in Table 7.2.3.6.1.
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 04/06/2017 8:36 AM, Travis Mack, SET wrote:

It can be R or I occupancy.  It doesn't matter.  It is the fact you are
protecting a dwelling unit with a dry pipe system.

7.2.3.6.3 For dry pipe systems protecting dwelling unit portions of any
occupancy, the sprinklers in the dwelling unit shall have a maximum water
delivery time of 15 seconds to the
single most remote sprinkler.

It seems like you have 15 seconds regardless.  Now, if you have a dry pipe
valve on the first floor and I believe you said these were on the 5th floor,
it seems quite unlikely you will get 15 seconds.  My suggestion is to find a
way to supply these sprinklers in the dwelling units from a wet pipe system.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 4/6/2017 8:16 AM, Dewayne Martinez wrote:
That was one of my concerns also. R-2 floor occupancy, calculating it per
light hazard but using residential heads.  If the R-2 occupancy is what
would dictate the 15sec delivery time then it wouldn't matter what type of
heads I used in the residential areas.

From: Sprinklerforum [mailto:[email protected]
<mailto:[email protected]%3cmailto:sprinklerfor
[email protected]>
<mailto:[email protected]>] On Behalf Of Travis
Mack
Sent: Thursday, April 06, 2017 8:58 AM
To: [email protected]
<mailto:[email protected]%3cmailto:sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers

Double check delivery times. I think you need a 15 second delivery time in
residential areas.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 6, 2017, at 6:31 AM, Dewayne Martinez <[email protected]
<mailto:[email protected]%3cmailto:[email protected]
om> <mailto:[email protected]>> wrote:
The dry portion below the attic was laid out at max 15x15 spacing with the
lines at 15ft above the floor.  The way the rooms layout there are long
runs with 8ft ceilings so I was going to drop down once to feed all these
rooms with one line but I still need to size it.  This reviewer will still
make us calculate the residential build out portion.  I can get by with a
1 1/4" line calculating  4 heads.

-----Original Message-----
From: Mark Phillips [mailto:[email protected]]
Sent: Thursday, April 06, 2017 8:17 AM
To: [email protected]
<mailto:[email protected]%3cmailto:sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>
Cc: [email protected]
<mailto:[email protected]%3cmailto:[email protected]
om> <mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers

If I'm understanding
The roof system is unchanged and your adding a lower supply to be rooms.

Use standard qr heads and same pipe sizes

The roof is still most demanding

Sent from my Verizon 4G LTE Droid
On Apr 6, 2017 9:14 AM, Dewayne Martinez <[email protected]
<mailto:[email protected]%3cmailto:[email protected]
om> <mailto:[email protected]>>
wrote:
NFPA 13 (07ed)

I have an existing 5th floor shell space that is installed as a light
hazard dry system that has pipe in the shell space and in the attic.  They
are turning this floor into a dormitory (R-2).
1)Can I use listed residential heads on return bends and only pick up 4
heads per 11.3.1.1 or will I need to pick up 1950SF?  What if there are
incidental areas such as a laundry room, ect. in the same areas as the
dorm rooms?
2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for
residential or 60sec for light hazard?

Thanks,
Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]
<mailto:[email protected]%3cmailto:[email protected]
om%3e%3cmailto:[email protected]>
<mailto:[email protected]><mailto:[email protected]
m>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]] [cid:[email protected]]
[cid:[email protected]]  [Top Workplaces 2015]

TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]%3cmailto:Sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




_______________________________________________

Sprinklerforum mailing list

[email protected]
<mailto:[email protected]%3cmailto:Sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________

Sprinklerforum mailing list

[email protected]
<mailto:[email protected]%3cmailto:Sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/5700c6e5/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 2712 bytes
Desc: image001.gif
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/5700c6e5/attachment-0001.gif>

------------------------------

Message: 3
Date: Thu, 6 Apr 2017 11:47:14 -0500
From: "Ed Kramer" <[email protected] <mailto:[email protected]> >
To: <[email protected]
<mailto:[email protected]> >
Subject: RE: NFPA 13 dry system - residential sprinklers
Message-ID: <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="utf-8"

A couple of things to consider:

-        Section 8.4.5.2 ? can?t use residential sprinks on a dry system
unless specifically listed for dry systems.

-        Section 8.3.4.1(2) ? Unless the pipe is galvanized or otherwise
corrosion resistant, minimum K-factor is 5.6.  

 

So you?ll need a residential sprink that is listed for dry systems and is
K5.6 or greater.

 

Ed Kramer

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Dewayne Martinez
Sent: Thursday, April 06, 2017 8:13 AM
To: [email protected]
<mailto:[email protected]> 
Cc: [email protected] <mailto:[email protected]> 
Subject: NFPA 13 dry system - residential sprinklers

 

NFPA 13 (07ed)

 

I have an existing 5th floor shell space that is installed as a light hazard
dry system that has pipe in the shell space and in the attic.  They are
turning this floor into a dormitory (R-2).

1)Can I use listed residential heads on return bends and only pick up 4
heads per 11.3.1.1 or will I need to pick up 1950SF?  What if there are
incidental areas such as a laundry room, ect. in the same areas as the dorm
rooms?

2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for
residential or 60sec for light hazard?    

 

Thanks,

Dewayne Martinez

Fire Protection Design Manager

 

TOTAL Mechanical

Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected] <mailto:[email protected]>
<mailto:[email protected]> 

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/

 

            

 

TOTAL Mechanical voted ?Top Workplace? for a 4th consecutive year. 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/fd289b6d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1497 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/fd289b6d/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1694 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/fd289b6d/attachment-0005.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1991 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/fd289b6d/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2347 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/fd289b6d/attachment-0007.jpeg>

------------------------------

Message: 4
Date: Thu, 6 Apr 2017 18:02:22 +0000
From: Gregory Lindholm <[email protected] <mailto:[email protected]> >
To: "[email protected]
<mailto:[email protected]> "
        <[email protected]
<mailto:[email protected]> >
Subject: Retail Building
Message-ID:
 
<dm5pr11mb170644e888d952f01fae0338d5...@dm5pr11mb1706.namprd11.prod.outlook.
com
<mailto:dm5pr11mb170644e888d952f01fae0338d5...@dm5pr11mb1706.namprd11.prod.o
utlook.com> >
        
Content-Type: text/plain; charset="iso-8859-1"

Something just came up here.


What would stop someone from saying that any retail store (Small Strip Mall,
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which
calls for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary
Hazard Group II?


Greg Lindholm
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/26aa7667/attachment-0001.htm>

------------------------------

Message: 5
Date: Thu, 6 Apr 2017 12:05:11 -0600
From: "Bob" <[email protected] <mailto:[email protected]> >
To: <[email protected]
<mailto:[email protected]> >
Subject: RE: Retail Building
Message-ID: <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="us-ascii"

Retail vs Mercantile?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: [email protected]
<mailto:[email protected]> 
Subject: Retail Building

 

Something just came up here. 

 

What would stop someone from saying that any retail store (Small Strip Mall,
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which
calls for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary
Hazard Group II?

 

Greg Lindholm 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/cac8f112/attachment-0001.htm>

------------------------------

Message: 6
Date: Thu, 6 Apr 2017 18:10:55 +0000
From: "Fox, Duane T. (FireMarshal)" <[email protected]
<mailto:[email protected]> >
To: "'[email protected]'" <[email protected]
<mailto:[email protected]> >,
        "'[email protected]'"
        <[email protected]
<mailto:[email protected]> >
Subject: RE: Retail Building
Message-ID:
        <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="us-ascii"

There is no such occupancy in NFPA 101 called Retail.  They are all
mercantile.  The difference is the height of storage on the shelving.  Group
II limits the height of storage to 12'.  If your Mercantile has shelving
storage that exceeds 12' then 20.3 would apply.  Good luck.

Duane T. Fox, Jr., CFPS, CFI, CFPE
Asst Chief, Technical Services
DE State Fire Marshal's Office



From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Thursday, April 06, 2017 2:05 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Retail Building

Retail vs Mercantile?

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: [email protected]
<mailto:[email protected]%3cmailto:sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>
Subject: Retail Building


Something just came up here.



What would stop someone from saying that any retail store (Small Strip Mall,
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which
calls for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary
Hazard Group II?


Greg Lindholm
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/2bffaf47/attachment-0001.htm>

------------------------------

Message: 7
Date: Thu, 6 Apr 2017 20:12:56 +0000
From: Steve Leyton <[email protected]
<mailto:[email protected]> >
To: "[email protected] <mailto:[email protected]> "
<[email protected] <mailto:[email protected]> >,
        "[email protected]
<mailto:[email protected]> "
        <[email protected]
<mailto:[email protected]> >
Subject: RE: Retail Building
Message-ID:
 
<mwhpr17mb11651c417a0a435922541e84d5...@mwhpr17mb1165.namprd17.prod.outlook.
com
<mailto:mwhpr17mb11651c417a0a435922541e84d5...@mwhpr17mb1165.namprd17.prod.o
utlook.com> >
        
Content-Type: text/plain; charset="us-ascii"

Mercantile (Group M) is how retail is classified in the building code.   For
our purposes Retail = Mercantile = Store = Dispensary (In Colorado,
Washington and select other states).

Obviously there are exceptions.  Stores with racks, tire stores, other
higher combustible-loaded "retail" uses require more robust fire protection.
But if you are confused about reference to an occupancy as Mercantile, it is
usually (and that's USUALLY with emphasis) an OH2.

My opinion only,
Steve L.


From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Thursday, April 6, 2017 11:05 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Retail Building

Retail vs Mercantile?

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregory Lindholm
Sent: Thursday, April 06, 2017 12:02 PM
To: [email protected]
<mailto:[email protected]%3cmailto:sprinklerforum@lists
.firesprinkler.org> <mailto:[email protected]>
Subject: Retail Building


Something just came up here.



What would stop someone from saying that any retail store (Small Strip Mall,
etc.) would have to be designed according to NFPA #13 - 2016 20.3, which
calls for .6 / 2000 for "Retail Store"??, instead of the normal Ordinary
Hazard Group II?


Greg Lindholm
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/355a575a/attachment-0001.htm>

------------------------------

Message: 8
Date: Thu, 6 Apr 2017 20:20:33 +0000
From: "Colin Carew (Cambridge)" <[email protected]
<mailto:[email protected]> >
To: "[email protected]
<mailto:[email protected]> "
        <[email protected]
<mailto:[email protected]> >
Subject: NFPA 20 4.7.7.2 
Message-ID:
 
<cy1pr07mb258890c58e0eb63d42c5b526f7...@cy1pr07mb2588.namprd07.prod.outlook.
com>
        
Content-Type: text/plain; charset="us-ascii"

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/9eb25937/attachment-0001.htm>

------------------------------

Message: 9
Date: Thu, 6 Apr 2017 16:27:51 -0400
From: John Irwin <[email protected]
<mailto:[email protected]> >
To: "[email protected]
<mailto:[email protected]> "
        <[email protected]
<mailto:[email protected]> >
Subject: RE: NFPA 20 4.7.7.2
Message-ID: <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="us-ascii"

Diesel pump? Otherwise no main relief allowed.



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]
<mailto:[email protected]> 
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and
punctuation gaffes.


-------- Original message --------
From: "Colin Carew (Cambridge)" <[email protected]
<mailto:[email protected]> >
Date: 4/6/17 4:20 PM (GMT-05:00)
To: [email protected]
<mailto:[email protected]> 
Subject: NFPA 20 4.7.7.2

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/eef42704/attachment-0001.htm>

------------------------------

Message: 10
Date: Thu, 6 Apr 2017 20:31:32 +0000
From: "Prahl, Craig/GVL" <[email protected] <mailto:[email protected]>
>
To: "[email protected]
<mailto:[email protected]> "
        <[email protected]
<mailto:[email protected]> >
Subject: RE: NFPA 20 4.7.7.2 
Message-ID:
 
<bn6pr06mb3043fde56361525a52e85e75d6...@bn6pr06mb3043.namprd06.prod.outlook.
com
<mailto:bn6pr06mb3043fde56361525a52e85e75d6...@bn6pr06mb3043.namprd06.prod.o
utlook.com> >
        
Content-Type: text/plain; charset="us-ascii"

Is the 140 psi total pressure or pump rating?

The pressure relief valve comes into play if the combination of supply
pressure and pump pressure exceeds the allowable system pressure, which for
most cases is 175 psi.

So if you had fluctuating supply pressures, during a higher than normal
pressure event, the system could relieve and not damage your downstream, 175
psi rated system.

Is this a diesel or electric?

How much pressure do you need at these heads?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected] <mailto:[email protected]> 


From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Colin Carew (Cambridge)
Sent: Thursday, April 06, 2017 4:21 PM
To: [email protected]
<mailto:[email protected]> 
Subject: NFPA 20 4.7.7.2 [EXTERNAL]

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/aa5da393/attachment-0001.htm>

------------------------------

Message: 11
Date: Thu, 6 Apr 2017 16:34:14 -0400
From: "Tom Duross" <[email protected] <mailto:[email protected]> >
To: <[email protected]
<mailto:[email protected]> >
Subject: RE: NFPA 20 4.7.7.2 
Message-ID: <[email protected]
<mailto:[email protected]> >
Content-Type: text/plain; charset="us-ascii"

Looks like you could be above 200 PSI churn or system pressure.  The
standard (2013 referenced) does not allow you to use the relief as a means
of blowing off excess pressure above 175.

Tom

 

Is the 140 psi total pressure or pump rating?

 

The pressure relief valve comes into play if the combination of supply
pressure and pump pressure exceeds the allowable system pressure, which for
most cases is 175 psi.

 

So if you had fluctuating supply pressures, during a higher than normal
pressure event, the system could relieve and not damage your downstream, 175
psi rated system.

 

Is this a diesel or electric?

 

How much pressure do you need at these heads?

 


Craig L. Prahl 



 

Hi Forum , 

 

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone . 

 

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being 

Used but 4.7.7.2 is  causing me to scratch my head . 

 

 

Colin 

 

 

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170406/b8964cef/attachment.htm>

------------------------------

Subject: Digest Footer

_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


------------------------------

End of Sprinklerforum Digest, Vol 49, Issue 3
*********************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to