> 20.3 is an alternative to the Chapter 16 and Chapter 17 requirements for “Big 
> Box” retail stores; likely as another way to avoid in-rack sprinklers.
>  
> The “…shall be permitted…” in paragraph 20.3.1 is key.  The designer has the 
> option of using the provisions of 20.3.1 if they meet all 13 of the following 
> conditions.  It does not mean the designer is required to meet the two 
> separate design points of 20.3.1.  The designer still has the option of 
> designing the system as per Chapter 16 or Chapter 17.  
>  
>  