If I understand you correctly, you just have a rack system with a separate riser. Flow the rack and overhead sprinklers and let the computer balance at the common junction point, wherever that is.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 4/11/2017 3:35 PM, [email protected] wrote:
I have been asked to look at a location which has 2 rack levels of pallets storage over garage doors in a loading dock area (existing). The rack sprinklers are presently fed from the existing wet ceiling system. Due to freeze ups and mechanical damage issues, they would like to feed to rack sprinklers from an adjacent pre-action system. Is there any issue with this and how would I handle the hydraulic calculations?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 <tel:860-535-2080> (ofc)
860-553-3553 <tel:860-553-3553> (fax)
860-608-4559 <tel:860-608-4559> (cell)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to