I don't recall anything in the standard against it. I admit I have never seen 
it. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Apr 11, 2017, at 3:40 PM, [email protected] wrote:
> 
> That was my initial thought, but I want to be sure there is not going to be 
> an issue with  mixing wet ceiling and double interlock pre-action rack 
> systems. 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-553-3553 (fax)
> 860-608-4559 (cell)
> 
> 
>> On Apr 11, 2017 at 6:36 PM, <SET Travis Mack> wrote:
>> 
>> If I understand you correctly, you just have a rack system with a separate 
>> riser.  Flow the rack and overhead sprinklers and let the computer balance 
>> at the common junction point, wherever that is.
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>> 
>> http://www.mfpdesign.com
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to us via: https://www.hightail.com/u/MFPDesign  
>> LinkedIn: https://www.linkedin.com/in/travismack
>>> On 4/11/2017 3:35 PM, [email protected] wrote:
>>> I have been asked to look at a location which has 2 rack levels of pallets 
>>> storage over garage doors in a loading dock area (existing). The rack 
>>> sprinklers are presently fed from the existing wet ceiling system. Due to 
>>> freeze ups and mechanical damage issues, they would like to feed to rack 
>>> sprinklers from an adjacent pre-action system. Is there any issue with this 
>>> and how would I handle the hydraulic calculations?
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> 860-535-2080 (ofc)
>>> 860-553-3553 (fax)
>>> 860-608-4559 (cell)
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to