That was my initial thought, but I want to be sure there is not going to be an 
issue with    mixing wet ceiling and double interlock pre-action rack systems.  
   
 
 Todd G Williams, PE 
Fire Protection Design/Consulting
 
Stonington, CT
 
860-535-2080 (tel:860-535-2080)  (ofc)
 
860-553-3553 (tel:860-553-3553)  (fax)
 
860-608-4559 (tel:860-608-4559)  (cell)
 
 
 
 
 

 
 
>  
> On Apr 11, 2017 at 6:36 PM,  <SET Travis Mack (mailto:[email protected])>  
> wrote:
>  
>  
>    
>
> If I understand you correctly, you just have a rack system with a separate 
> riser.    Flow the rack and overhead sprinklers and let the computer balance 
> at the common junction point, wherever that is.
>
>
>  
>  Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 
> 480-505-9271 fax: 866-430-6107  email:[email protected] 
> (mailto:email:[email protected])   http://www.mfpdesign.com   
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692  Send large files 
> to us via:  https://www.hightail.com/u/MFPDesign  LinkedIn:  
> https://www.linkedin.com/in/travismack  
>  
> On 4/11/2017 3:35 PM,  [email protected] (mailto:[email protected])  
> wrote:
>  
> >  
> >  
> > I have been asked to look at a location which has 2 rack levels of pallets 
> > storage over garage doors in a loading dock area (existing). The rack 
> > sprinklers are presently fed from the existing wet ceiling system. Due to 
> > freeze ups and mechanical damage issues, they would like to feed to rack 
> > sprinklers from an adjacent pre-action system. Is there any issue with this 
> > and how would I handle the hydraulic calculations?
> >    
> >  
> >  Todd G Williams, PE 
> > Fire Protection Design/Consulting
> >  
> > Stonington, CT
> >  
> > 860-535-2080 (tel:860-535-2080)  (ofc)
> >  
> > 860-553-3553 (tel:860-553-3553)  (fax)
> >  
> > 860-608-4559 (tel:860-608-4559)  (cell)
> >  
> >  
> >  
> >  
> >    
> >  
> >  _______________________________________________ Sprinklerforum mailing 
> > list  [email protected] 
> > (mailto:[email protected])   
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >   
>
>  
>  
 
 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to