If your using 2016 code the 6" rule is pretty much eliminated in CA

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Monday, September 18, 2017 8:27 PM
To: [email protected]
Subject: RE: CPVC Seismic

 

I had to step out for a couple of hours, but I'm back.

I'm assuming that I can use the rods less than 6" rule and omit lateral
bracing, right?

That would leave 4-ways and longitudinal only, correct?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of MFP Design, LLC
Sent: Monday, September 18, 2017 4:31 PM
To: [email protected]; [email protected]
Subject: RE: CPVC Seismic

 

Really no different.  I doubt you will find longitudinal bracing listed for
cpvc.  You will have to put a short branch (same size as main) perpendicular
to the main and brace that with a lateral brace to act as your longitudinal
brace on the main.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Monday, September 18, 2017 3:28 PM
To: [email protected]
Subject: CPVC Seismic

 

I'm about to do my first CPVC sway bracing calc's.  This is in CA (a first
for me as well), north of San Francisco.  

Are there any special issues that I need to consider, or do I approach this
as if it's not much different than if it where steel?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

FBK-LOGO-SMALL

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to