What city in northern CA is letting you get away with 2013 code?

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information 

belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Monday, September 18, 2017 8:46 PM
To: [email protected]
Subject: RE: CPVC Seismic

 

Using 2013, and the area of concern will be supported with 2-hole CPVC straps.

 

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Monday, September 18, 2017 9:43 PM
To: [email protected]; [email protected]
Subject: Re: CPVC Seismic

 

What is your edition of NFPA 13. If you are in the 2016 edition don't 
automatically assume you can eliminate due to clearances less than 6". There 
are cases where you don't. 

 

Also note in older editions it is 6" from top of pipe to point of connection to 
structure. 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Sep 18, 2017, at 8:26 PM, Bob <[email protected]> wrote:

I had to step out for a couple of hours, but I’m back.

I’m assuming that I can use the rods less than 6” rule and omit lateral 
bracing, right?

That would leave 4-ways and longitudinal only, correct?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Monday, September 18, 2017 4:31 PM
To: [email protected]; [email protected]
Subject: RE: CPVC Seismic

 

Really no different.  I doubt you will find longitudinal bracing listed for 
cpvc.  You will have to put a short branch (same size as main) perpendicular to 
the main and brace that with a lateral brace to act as your longitudinal brace 
on the main.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Monday, September 18, 2017 3:28 PM
To: [email protected]
Subject: CPVC Seismic

 

I’m about to do my first CPVC sway bracing calc’s.  This is in CA (a first for 
me as well), north of San Francisco.  

Are there any special issues that I need to consider, or do I approach this as 
if it’s not much different than if it where steel?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

<image001.jpg>

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to