I like what Ryan suggests.  I have also  seen it requested that if sch 40
is required it will be cut grooved for pipe 2” and larger and that all
installed piping shall either be seamless or must be fabricated with the
seam not on the bottom.  My fabricator said this would not be a problem as
long as they knew about it prior to fabrication.



Dewayne Martinez

Fire Protection Design Manager



*TOTAL* *Mechanical*

*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

*http://www.total-mechanical.com/ <http://www.total-mechanical.com/>*



[image: Consecutive Honors 2012-2017]







*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Hinson, Ryan
*Sent:* Tuesday, October 03, 2017 1:18 PM
*To:* [email protected]
*Subject:* RE: Schedule 10 vs Schedule 40 pipe



I would say to use nitrogen in lieu of shop air and then use schedule 10
for sizes larger than 2”.



*Ryan L. Hinson**, PE*, SET***  \  Burns & McDonnell

Senior Fire Protection Engineer

*O* 952-656-3662 \  *M* 320-250-5404  \  *F* 952-229-2923

*[email protected] <[email protected]>*  \  burnsmcd.com
<http://www.burnsmcd.com/>

8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437

*Registered in: LA, MD, MN, PA, TX, & UT

**NICET IV - Water-Based Systems Layout



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *Mike
Stossel
*Sent:* Tuesday, October 03, 2017 12:50 PM
*To:* [email protected]
*Subject:* RE: Schedule 10 vs Schedule 40 pipe



In my opinion if the schedule 40 is going to be grooved than it would
probably be worth it, but if they are going to thread the schedule 40 than
schedule 10 will most likely outlast the 40. I am basing this on schedule
10 grooved piping having a better corrosion resistance ration than threaded
schedule 40.



Mike Stossel *SET*

[image: 400dpiLogoCropped]

36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

[email protected]



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *John
Paulsen
*Sent:* Tuesday, October 3, 2017 1:34 PM
*To:* [email protected]
*Subject:* Schedule 10 vs Schedule 40 pipe



Hello Forumites:



We are working to develop a bid package for a pair of large freezers and
coolers used for food stuffs storage on racks to 35’. The freezers are to
be -10 degrees and the coolers will be 31 degrees. The sprinklers systems
will be double interlock pre-action with Protecto-wire detection and CMSA
sprinklers.



My question:     The owner is asking for a recommendation on whether to
spec schedule 10 or schedule 40 piping. The concern is long term
serviceability of the piping system. My initial thought is that due to the
constant low ambient temperatures corrosion would be seriously inhibited
for two reasons; any condensate in the pipe would be in frozen form and the
low temps would inhibit microbial growth. So my thought is that schedule 10
pipe would last the 20 year expected service life of the system. However, I
would like to get the thoughts of the forum participants, is the cost of
schedule 40 warranted or would schedule 10 service just as well in this
application?



Thanks in advance for your responses.



John Paulsen – SET