Hi John,

The most effective measure would be cut grooved sch. 40 black steel using 
Nitrogen as your supervisory gas instead of shop air. This will eliminate the 
dam effect at the joint. However, the biggest value for your customer will 
likely be roll grooved sch. 10 black steel and still using Nitrogen as your 
supervisory gas.

Many arguments can be made about the CRR value which is nothing more than a 
comparison of the thickness of schedule 40 pipe under the first exposed thread. 
The "first exposed thread" is the minimum pipe thickness exposed to both 
interior and exterior corrosion. It occurs at the threaded joint at a line 
defined by the thread width just before the pipe engages the fitting. There are 
too many factors to consider when identifying corrosion rates and this ratio is 
very subjective. Strictly a comparison.

As for using Nitrogen as a supervisory gas I think this is definitely the 
biggest "bang for your buck". In your particular instance Nitrogen provides you 
with more than just a corrosion mitigation solution. In particular the low 
dewpoint of 98%+ N2. A typical refrigerated dryer will only get you somewhere 
around -40°F dew point and 98% Nitrogen will be somewhere around -60°F dew 
point (that's a 50% increase in humidity reduction).

Hope you find this helpful.

Andy L. Kaempfer
Senior Application Engineer - Fire Protection Systems
Bull Moose Tube Company
1819 Clarkson Road
Chesterfield, MO  63017
O: 636-812-9276
F:  636-530-5880
M: 314-306-2471
[BullMooseCorporateTagline-black]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Tuesday, October 3, 2017 12:34 PM
To: [email protected]
Subject: Schedule 10 vs Schedule 40 pipe

Hello Forumites:

We are working to develop a bid package for a pair of large freezers and 
coolers used for food stuffs storage on racks to 35'. The freezers are to be 
-10 degrees and the coolers will be 31 degrees. The sprinklers systems will be 
double interlock pre-action with Protecto-wire detection and CMSA sprinklers.

My question:     The owner is asking for a recommendation on whether to spec 
schedule 10 or schedule 40 piping. The concern is long term serviceability of 
the piping system. My initial thought is that due to the constant low ambient 
temperatures corrosion would be seriously inhibited for two reasons; any 
condensate in the pipe would be in frozen form and the low temps would inhibit 
microbial growth. So my thought is that schedule 10 pipe would last the 20 year 
expected service life of the system. However, I would like to get the thoughts 
of the forum participants, is the cost of schedule 40 warranted or would 
schedule 10 service just as well in this application?

Thanks in advance for your responses.

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206

Disclaimer

The information contained in this communication from the sender is 
confidential. It is intended solely for use by the recipient and others 
authorized to receive it. If you are not the recipient, you are hereby notified 
that any disclosure, copying, distribution or taking action in relation of the 
contents of this information is strictly prohibited and may be unlawful.

This email has been scanned for viruses and malware, and may have been 
automatically archived by Mimecast Ltd, an innovator in Software as a Service 
(SaaS) for business. Providing a safer and more useful place for your human 
generated data. Specializing in; Security, archiving and compliance. To find 
out more visit the Mimecast website.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to