Ok. I’ll bite.   This is all anecdotal, but I’ve seen the inside of pipe in 
several nearly 20 year old, -10 deg. F.  freezer systems.  The reason we were 
tearing into these systems was because of ice plugs.  Pics from some of our 
systems were flying around FM as they were coming up with ways to solve the 
problem.  Those methods eventually made it into NFPA 13 (2013) 7.9.2.7.   I’ve 
also seen the inside of way too many plugged dry systems as you describe.  I 
don’t remember corrosion ever being an issue in the freezers.  Most of these 
systems were sched 10.

When we pulled the supply air from the cold area, and added isolation valves 
above the preaction valves for the trip tests, we solved most of the problem.  
Some customers went further and had us add regenerative desiccant dryers.  
While I have no experience with nitrogen systems, I suspect they’re the best 
solution for the dew point reasons previously stated.  However, I’ve wondered 
how expensive they are to maintain when supplying large, loose systems.  Most 
of the systems we dealt with also had in-rack sprinklers with pipe that was 
abused by forklifts.  We believed that this abuse led to leaks – especially at 
the grooved couplings.  We thought we solved that problem by replacing ‘older’ 
couplings with couplings with gap seal type gaskets rated for the cold.  I’m 
guessing the ‘rated for cold’ was more important than the ‘gap seal’ part in 
these areas that never see above -10F.

Based on my experience, corrosion wasn’t an issue and believe me, I’ve seen it 
all as far as mini-dammed sched 10 dry systems becoming plugged and ‘porous’.  
Many years ago on this forum,  after preaching about the horrors of roll 
grooved mini-dams in dry systems, I received the nickname “Mini Dam Dave” from 
a frequent poster (miss you George!).   For a ceiling only freezer system, even 
the big ones,  I’d be comfortable with sched 10, proper gaskets in grooved 
coups, tank mounted air compressor,  with sprinkler and air supply pipes per 
the diagrams in NFPA13.  Should one become necessary, I’d spec provisions/room 
for the addition of a dryer or nitrogen generator. For a large system with 
IRAS, I’d spec the dryer/nitrogen up front.

Dave Sornsin
Formerly Fargo, ND
Currently Kent, WA
701.371.0643

Sornsin Fire Protection
FPS, LLC



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Wednesday, October 04, 2017 7:13 AM
To: [email protected]
Subject: RE: Schedule 10 vs Schedule 40 pipe

Thanks guys, I DO find all of this helpful, but I was hoping to hear from 
someone that had experience with the “environmental” conditions of this freezer 
project and if they had noticed that the constant freezing conditions had 
inhibited corrosion in the pipes.

I agree that under normal freeze thaw cycles, periodic trip testing and 
condensate water held in the pipe by roll grooves would best be controlled by 
all of the points mentioned in the thread. I have seen SO many horror stories 
in attics over the years with plugged lines from fine scale being compacted 
more at every trip test. I have no trouble explaining to clients why the 
internal inspection of their system is a critical “must do” maintenance item. 
But I would like to keep the pipe sizes on this project as small as possible in 
order to meet the trip times required by the CMSA head that we are using. If we 
spec schedule 40, it essentially increases the pipe size a diameter.

If it’s justified I will do so. But I have this nagging doubt that the freezing 
temps will preserve the schedule 10… if the seams are fabbed on top of course…

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Andy Kaempfer
Sent: Wednesday, October 4, 2017 9:36 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Schedule 10 vs Schedule 40 pipe

Hi John,

The most effective measure would be cut grooved sch. 40 black steel using 
Nitrogen as your supervisory gas instead of shop air. This will eliminate the 
dam effect at the joint. However, the biggest value for your customer will 
likely be roll grooved sch. 10 black steel and still using Nitrogen as your 
supervisory gas.

Many arguments can be made about the CRR value which is nothing more than a 
comparison of the thickness of schedule 40 pipe under the first exposed thread. 
The “first exposed thread” is the minimum pipe thickness exposed to both 
interior and exterior corrosion. It occurs at the threaded joint at a line 
defined by the thread width just before the pipe engages the fitting. There are 
too many factors to consider when identifying corrosion rates and this ratio is 
very subjective. Strictly a comparison.

As for using Nitrogen as a supervisory gas I think this is definitely the 
biggest “bang for your buck”. In your particular instance Nitrogen provides you 
with more than just a corrosion mitigation solution. In particular the low 
dewpoint of 98%+ N2. A typical refrigerated dryer will only get you somewhere 
around -40°F dew point and 98% Nitrogen will be somewhere around -60°F dew 
point (that’s a 50% increase in humidity reduction).

Hope you find this helpful.

Andy L. Kaempfer
Senior Application Engineer – Fire Protection Systems
Bull Moose Tube Company
1819 Clarkson Road
Chesterfield, MO  63017
O: 636-812-9276
F:  636-530-5880
M: 314-306-2471
[BullMooseCorporateTagline-black]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Tuesday, October 3, 2017 12:34 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Schedule 10 vs Schedule 40 pipe

Hello Forumites:

We are working to develop a bid package for a pair of large freezers and 
coolers used for food stuffs storage on racks to 35’. The freezers are to be 
-10 degrees and the coolers will be 31 degrees. The sprinklers systems will be 
double interlock pre-action with Protecto-wire detection and CMSA sprinklers.

My question:     The owner is asking for a recommendation on whether to spec 
schedule 10 or schedule 40 piping. The concern is long term serviceability of 
the piping system. My initial thought is that due to the constant low ambient 
temperatures corrosion would be seriously inhibited for two reasons; any 
condensate in the pipe would be in frozen form and the low temps would inhibit 
microbial growth. So my thought is that schedule 10 pipe would last the 20 year 
expected service life of the system. However, I would like to get the thoughts 
of the forum participants, is the cost of schedule 40 warranted or would 
schedule 10 service just as well in this application?

Thanks in advance for your responses.

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438
F – 614-782-2374
C – 614-348-8206




Disclaimer

The information contained in this communication from the sender is 
confidential. It is intended solely for use by the recipient and others 
authorized to receive it. If you are not the recipient, you are hereby notified 
that any disclosure, copying, distribution or taking action in relation of the 
contents of this information is strictly prohibited and may be unlawful.

This email has been scanned for viruses and malware, and may have been 
automatically archived by Mimecast Ltd, an innovator in Software as a Service 
(SaaS) for business. Providing a safer and more useful place for your human 
generated data. Specializing in; Security, archiving and compliance. To find 
out more Click Here<http://www.mimecast.com/products/>.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to