I'm working on building permit plans for a job, and the architect passed on
an email from their accessibility consultant that the fire department hose
valves can't protrude beyond the standpipe riser more than 4", per ANSI
A117.1 figure 307.3. The text of that section is:

307.3 Post-Mounted Objects. Objects on posts or pylons shall be permitted
to overhang 4 inches (100 mm) maximum where more than 27 inches (685 mm)
and not more than 80 inches (2030 mm) above the floor. Objects on multiple
posts or pylons where the clear distance between the posts or pylons is
greater than 12 inches (305 mm) shall have the lowest edge of such object
either 27 inches (685 mm) maximum or 80 inches (2030 mm) minimum above the
floor.

What they're saying is that we will need to turn an elbow up from the
outlet of the standpipe and install the valve vertical. I've already told
them this won't work anyway, since the valve itself has a 5" hand wheel,
and due to takeouts, the least amount of projection physically possible is
about 8". According to the consultant, the way to mitigate this is to
install cane protection, which the architect appears to want to avoid. Is
anyone aware of this code section, and does it apply the way I'm being told
it does? In nearly 13 years as a designer, I've never been told such a
requirement exists.


James
Charlotte, NC