Unfortunately other than the fact that the drawings in the 3## section 
make it pretty obvious this isn't what they're talking about, there's no 
definitions.  I figured if its a stairwell it's an easier shoot down for 
someone who wants to write their own interpretations since the conspicuous 
absence of stairs in pretty much this entire standard should make it 
pretty open and shut.  You could argue its not those things and that the 
previous section says leading edge, which the leading edge of the handle 
if you put it parallel to the floor probably isn't more than 4" out. 
Basically this code section is to keep someone tapping a cane against the 
edge of the walking path from slamming into some random protruding object, 
if they hit the hand wheel it may not be super pleasant but its not the 
kind of protrusion, IMHO, this section addresses.  Just one of those fun 
common sense vs power trip things probably.  Standard disclaimer, these 
are my opinions only and have not been approved or reviewed by my 
employer.



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   "rongreenman ." <[email protected]>
To:     [email protected]
Date:   11/14/2017 03:25 PM
Subject:        Re: ANSI A1171.1 Figure 307.3
Sent by:        "Sprinklerforum" 
<[email protected]>



Does the standard define the standpipe as a post or pylon?  

On Tue, Nov 14, 2017 at 12:10 PM Mike B Morey <[email protected]> 
wrote:
Where is the standpipe located?  Are we talking a typical stairwell 
install or elsewhere?  Section 307 starts off by stating that it governs 
circulation paths, and stairs aren't part of that definition in section 
1005 based on a quick look.  The standard is available several places 
online if you google it, not sure if they're "legal" copies but for the 
sake of answering the question I'd take a look at that angle.  If its in a 
hall or something I'd imagine it could be put in a box in the wall or 
something. 


Mike Morey 
CFPS 3229 • NICET S.E.T. 123677 
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company 
7614 Opportunity Drive • Fort Wayne, IN • 46825 
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:        James Litvak <[email protected]> 
To:        "[email protected]" <
[email protected]> 
Date:        11/14/2017 02:59 PM 
Subject:        ANSI A1171.1 Figure 307.3 
Sent by:        "Sprinklerforum" <
[email protected]> 



I'm working on building permit plans for a job, and the architect passed 
on an email from their accessibility consultant that the fire department 
hose valves can't protrude beyond the standpipe riser more than 4", per 
ANSI A117.1 figure 307.3. The text of that section is: 

307.3 Post-Mounted Objects. Objects on posts or pylons shall be permitted 
to overhang 4 inches (100 mm) maximum where more than 27 inches (685 mm) 
and not more than 80 inches (2030 mm) above the floor. Objects on multiple 
posts or pylons where the clear distance between the posts or pylons is 
greater than 12 inches (305 mm) shall have the lowest edge of such object 
either 27 inches (685 mm) maximum or 80 inches (2030 mm) minimum above the 
floor.  

What they're saying is that we will need to turn an elbow up from the 
outlet of the standpipe and install the valve vertical. I've already told 
them this won't work anyway, since the valve itself has a 5" hand wheel, 
and due to takeouts, the least amount of projection physically possible is 
about 8". According to the consultant, the way to mitigate this is to 
install cane protection, which the architect appears to want to avoid. Is 
anyone aware of this code section, and does it apply the way I'm being 
told it does? In nearly 13 years as a designer, I've never been told such 
a requirement exists.  


James 
Charlotte, NC_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=wiCt1iqr5u69Txm-iBELel0Xzd3F5uGuCJUQXBz1wqg&s=xRsf5UToNzmQSkkENHTI-JrcpESCaLYKnTi-kcXYGmg&e=


This message is for the named person's use only. It may contain 
confidential, proprietary or legally privileged information. No 
confidentiality or privilege is waived or lost by any mistransmission. If 
you receive this message in error, please immediately delete it and all 
copies of it from your system, destroy any hard copies of it and notify 
the sender. You must not, directly or indirectly, use, disclose, 
distribute, print, or copy any part of this message if you are not the 
intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
-- 
Sent from Gmail Mobile[attachment "attcgpkb.jpg" deleted by Mike B 
Morey/Shambaugh/EMCORGROUP] 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=5qwVwJLjSTa1NIX64A78M2wWVYYDHlGdPLp5aekf9Eg&s=hCvxa01YwdjeSk4O21JWnAfEVWaoF93WIMHJkrFr_lM&e=



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to