James:

I know this comes off sounding a little big-headed but …  I’m the chair of the 
committee and I’ve never heard of such balderdash.   This isn’t a “post” or a 
“pylon” – those are structures.   This is a pipe and part of a “building 
system” and also a part of the fire/life safety apparatus.   The applicable 
dimensions are the ones that define clear egress path on the landings (as per 
the building code) and the elevation above fin floor as prescribed in NFPA 14 
and/or per the responding fire agency.     Whether the ports point out, down at 
a 45° angle or straight down at the floor is also up to the responding fire 
agency.   I think your idea of getting an superseding opinion from the local 
AHJ (BO or FO) is sound.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Litvak
Sent: Tuesday, November 14, 2017 1:09 PM
To: [email protected]
Subject: Re: ANSI A1171.1 Figure 307.3

The standpipe is in a stairwell. Some of the stairs it'll be in the corner, 
others beside the door. All of them will be outside the required path of egress 
clearance. The definition of circulation path in A117.1 is "An exterior or 
interior way of passage from one place to another for pedestrians". It's pretty 
vague. Unfortunately there's no differentiation between, say, a hallway or a 
stairwell. I think I'll contact the building department and see what they 
think. Hopefully they'll write something for me saying that section doesn't 
apply.


On Tue, Nov 14, 2017 at 3:40 PM Mike B Morey 
<[email protected]<mailto:[email protected]>> wrote:
Unfortunately other than the fact that the drawings in the 3## section make it 
pretty obvious this isn't what they're talking about, there's no definitions.  
I figured if its a stairwell it's an easier shoot down for someone who wants to 
write their own interpretations since the conspicuous absence of stairs in 
pretty much this entire standard should make it pretty open and shut.  You 
could argue its not those things and that the previous section says leading 
edge, which the leading edge of the handle if you put it parallel to the floor 
probably isn't more than 4" out.  Basically this code section is to keep 
someone tapping a cane against the edge of the walking path from slamming into 
some random protruding object, if they hit the hand wheel it may not be super 
pleasant but its not the kind of protrusion, IMHO, this section addresses.  
Just one of those fun common sense vs power trip things probably.  Standard 
disclaimer, these are my opinions only and have not been approved or reviewed 
by my employer.

________________________________

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]<mailto:[email protected]>

[cid:_2_0846049C0846000C0071963C852581D8]





From:        "rongreenman ." 
<[email protected]<mailto:[email protected]>>
To:        
[email protected]<mailto:[email protected]>
Date:        11/14/2017 03:25 PM
Subject:        Re: ANSI A1171.1 Figure 307.3
Sent by:        "Sprinklerforum" 
<[email protected]<mailto:[email protected]>>
________________________________



Does the standard define the standpipe as a post or pylon?

On Tue, Nov 14, 2017 at 12:10 PM Mike B Morey 
<[email protected]<mailto:[email protected]>> wrote:
Where is the standpipe located?  Are we talking a typical stairwell install or 
elsewhere?  Section 307 starts off by stating that it governs circulation 
paths, and stairs aren't part of that definition in section 1005 based on a 
quick look.  The standard is available several places online if you google it, 
not sure if they're "legal" copies but for the sake of answering the question 
I'd take a look at that angle.  If its in a hall or something I'd imagine it 
could be put in a box in the wall or something.
________________________________

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]<mailto:[email protected]>







From:        James Litvak <[email protected]<mailto:[email protected]>>
To:        
"[email protected]<mailto:[email protected]>"
 
<[email protected]<mailto:[email protected]>>
Date:        11/14/2017 02:59 PM
Subject:        ANSI A1171.1 Figure 307.3
Sent by:        "Sprinklerforum" 
<[email protected]<mailto:[email protected]>>
________________________________



I'm working on building permit plans for a job, and the architect passed on an 
email from their accessibility consultant that the fire department hose valves 
can't protrude beyond the standpipe riser more than 4", per ANSI A117.1 figure 
307.3. The text of that section is:

307.3 Post-Mounted Objects. Objects on posts or pylons shall be permitted to 
overhang 4 inches (100 mm) maximum where more than 27 inches (685 mm) and not 
more than 80 inches (2030 mm) above the floor. Objects on multiple posts or 
pylons where the clear distance between the posts or pylons is greater than 12 
inches (305 mm) shall have the lowest edge of such object either 27 inches (685 
mm) maximum or 80 inches (2030 mm) minimum above the floor.

What they're saying is that we will need to turn an elbow up from the outlet of 
the standpipe and install the valve vertical. I've already told them this won't 
work anyway, since the valve itself has a 5" hand wheel, and due to takeouts, 
the least amount of projection physically possible is about 8". According to 
the consultant, the way to mitigate this is to install cane protection, which 
the architect appears to want to avoid. Is anyone aware of this code section, 
and does it apply the way I'm being told it does? In nearly 13 years as a 
designer, I've never been told such a requirement exists.


James
Charlotte, NC_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=wiCt1iqr5u69Txm-iBELel0Xzd3F5uGuCJUQXBz1wqg&s=xRsf5UToNzmQSkkENHTI-JrcpESCaLYKnTi-kcXYGmg&e=

This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=5qwVwJLjSTa1NIX64A78M2wWVYYDHlGdPLp5aekf9Eg&s=hCvxa01YwdjeSk4O21JWnAfEVWaoF93WIMHJkrFr_lM&e=>
--
Sent from Gmail Mobile[attachment "attcgpkb.jpg" deleted by Mike B 
Morey/Shambaugh/EMCORGROUP] _______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=5qwVwJLjSTa1NIX64A78M2wWVYYDHlGdPLp5aekf9Eg&s=hCvxa01YwdjeSk4O21JWnAfEVWaoF93WIMHJkrFr_lM&e=

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to