A standpipe is neither a post or pylon. Those are both protective barricades 
(have him/her look up the definitions). A standpipe is a working part of the 
building system. Not applicable.
 
 
 
 Todd G Williams, PE 
Fire Protection Design/Consulting
 
Stonington, CT
 
860-535-2080 (tel:860-535-2080)  (ofc)
 
860-553-3553 (tel:860-553-3553)  (fax)
 
860-608-4559 (tel:860-608-4559)  (cell)
 
 
 
 

 
 
>  
> On Nov 14, 2017 at 2:57 PM,  <James Litvak (mailto:[email protected])>  
> wrote:
>  
>  
>  
> I'm working on building permit plans for a job, and the architect passed on 
> an email from their accessibility consultant that the fire department hose 
> valves can't protrude beyond the standpipe riser more than 4", per ANSI 
> A117.1 figure 307.3. The text of that section is:
>  
>
>  
> 307.3 Post-Mounted Objects. Objects on posts or pylons shall be permitted to 
> overhang 4 inches (100 mm) maximum where more than 27 inches (685 mm) and not 
> more than 80 inches (2030 mm) above the floor. Objects on multiple posts or 
> pylons where the clear distance between the posts or pylons is greater than 
> 12 inches (305 mm) shall have the lowest edge of such object either 27 inches 
> (685 mm) maximum or 80 inches (2030 mm) minimum above the floor.  
>  
>
>  
> What they're saying is that we will need to turn an elbow up from the outlet 
> of the standpipe and install the valve vertical. I've already told them this 
> won't work anyway, since the valve itself has a 5" hand wheel, and due to 
> takeouts, the least amount of projection physically possible is about 8". 
> According to the consultant, the way to mitigate this is to install cane 
> protection, which the architect appears to want to avoid. Is anyone aware of 
> this code section, and does it apply the way I'm being told it does? In 
> nearly 13 years as a designer, I've never been told such a requirement 
> exists.  
>  
>
>  
>
>  
> James
>  
> Charlotte, NC
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  
 
 
 
 
 
 

 
 