Yes it is, but if there’s not much of it in the common piping before the first 
standpipe branches off then it’s less impactful.  The downstream part of it is 
obviously subjective and yes, if you’re pumping 1,000 GPM, 6” is preferred.   
Buy you’re not going to be seeing problems from velocity or turbulence once the 
water gets to the hose connections assuming min. 4” risers and 2½” valve 
connections to standpipes, so calc’ on Garth.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Charles Bamford
Sent: Friday, November 17, 2017 12:33 PM
To: [email protected]
Subject: Re: RE: FDC sizing on wet automatic standpipes

4" pipe for 1000 gpm is very restrictive

City of Redmond WA requires flow test,
and we just did one. Here are our results
Remote hose @                          100 psi  260 gpm  level 5
10' lower on same standpipe        104 psi 290 gpm   level 4
@ 2 other Restricted hose valves  110 psi 250 gpm
150 psi @ riser 1050 gpm
+-175 psi @ FDC on wall  level 1
+-200 psi @ pumper truck using 100' 5"dia. with 5" storz.

30' of 4"sch 10 from wall FDC to 6" tee then +-130 6"sch 10 to riser

6" or 8" FDC for underground supply would be nice.



On ‎Friday‎, ‎November‎ ‎17‎, ‎2017‎ ‎12‎:‎07‎:‎05‎ ‎PM‎ ‎PST, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:



Yeah, what Travis said.   Everyone should remember that FDC configurations and 
sizing take into account the chance that there may be obstruction or damage to 
an inlet, so providing four is not based on hydraulics only.    As for the pipe 
sizing … I have less energy about that and if it calc’s then it should be 
adequate.   But (and as per my usual rap)...



IT’S UP TO THE AHJ.



The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.



Steve Leyton

Protection Design & Consulting

San Diego, CA











From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Friday, November 17, 2017 12:03 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: FDC sizing on wet automatic standpipes



I don’t believe it matters what the building serves.  It is an automatic 
standpipe.  I don’t see in Chapter 7 of NFPA 14 2013 that says the FDC inlet 
shall be based on 250 gpm per inlet only if it is a manual standpipe.  I don’t 
see where you have to calculate through the FDC.  You may be able to use 4”, 
but you will still need 4 inlets.  I think that seems quite odd and would 
probably try to run it as 6” as a good practice.  However, I can’t see anything 
requiring the size of the piping to be any minimum.





[MFP_logo_F]

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>

https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>



“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”







From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, November 17, 2017 12:52 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: FDC sizing on wet automatic standpipes



Is this a residential or light hazard 8 story building?

Do you have a 1000 gpm fire pump from city water? Electric or diesel?

Reliable power with no outages?

3 - 4 or more standpipe risers?



Then you can get answers.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Friday, November 17, 2017 11:05 AM
To: 
[email protected]<mailto:[email protected]>
Subject: FDC sizing on wet automatic standpipes



I'm not lucky enough to be able to treat the FDC on a wet automatic standpipe 
as supplemental am I?

We have a building with a combined sprinkler and standpipe system that's wet 
automatic. Building is 8 stories, but separated. etc. etc.

Since the standpipe is wet automatic, the FDC isn't the only supply source, so 
do we still have to calculate it hydraulically? Total standpipe demand is 1000 
GPM

We're using NFPA 14, 2013 edition.

Basically, I'm trying to figure out if its OK to run 4" to the FDC and use a 
single Siamese instead of 6" piping to a 4-way or two Siamese connections.

Benjamin Young



[Image removed by 
sender.]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>


Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to