Our supply engines are rated 2000 gpm, attack engines 1000-1500 gpm. Notice I 
wrote rated, in many cases they can exceed those values.  As for an FDC the 
basic question comes down to; a) are the systems supplied by an automatic water 
source and thus the FDC is merely supplemental, b) are the systems supplied by 
the fire department and thus the FDC is the primary water source, c) some 
combination wherein the fire department is supplying a portion of the demand.

John

John Drucker, CET
Assistant Construction Official
Fire and Electrical Subcode Official
Building Inspector
Building Department
Borough of Red Bank, NJ
Cell/Text 732-904-6823
________________________________
From: Sprinklerforum [[email protected]] on behalf 
of Bruce Verhei [[email protected]]
Sent: Sunday, November 19, 2017 1:39 PM
To: [email protected]
Subject: Re: FDC sizing on wet automatic standpipes

A high percentage of municipal engines are rated at 1,500 gpm. The power plants 
all have excess power for pumping. You’ll see some 1,750 rated pumps. The are 
the same pump with another 2 1/2” discharge. I’m not sure the impeller is cut 
differently. You just run a little higher rpm.

The old Detroit Diesel 6-71 NA did fine pumping 1,500. Lots of engines have 
power plants nearly twice as powerful.

Best.

Bruce Verhei



On Nov 19, 2017, at 10:26, Pete Schwab 
<[email protected]<mailto:[email protected]>> wrote:

NFPA 14 requires that the piping to the FDC be sized to supply the system 
demand for manual and automatic standpipes. 7.7.1 is pretty clear and does not 
delineate between automatic or manual. Also see the 2016 edition section 
A.7.10.1.2. Just my opinion and not that of NFPA.

7.7 System Design and Sizing of Pipe for Delivery of System
Demand.
7.7.1 Class I and Class III standpipe systems shall be designed
so that the system demand can be supplied by each fire department
connection, which is provided in accordance with Section
7.12.
7.7.2* Where an automatic or semiautomatic water supply is
required for a Class I, II, or III standpipe system by Section 5.4,
the standpipe system shall be designed so that the system demand
can be independently supplied by the attached water
supply and each fire department connection provided on the
system.
7.7.3 Where a manual system is permitted by Section 5.4 and
an attached water supply is provided to supply an automatic
sprinkler system or to maintain water in a wet system, the attached
water supply shall not be required to satisfy the standpipe
system demand.
7.7.4 When the system demand to be supplied by the fire
department at the fire department connection is being determined,
the local fire department shall be consulted regarding
the water supply available from a fire department pumper.


When performing a hydraulic design, the hydraulic characteristics
of each water supply need to be known. The procedure
for determining the hydraulic characteristics of permanent
water supplies, such as pumps, is fairly straightforward and is
described in NFPA 20. The procedure for determining the
hydraulic characteristics of fire apparatus supplying a standpipe
system are similar. Lacking better information about local fire
apparatus, a conservative design would accommodate a
1000 gpm (3785 L/min) fire department pumper performing
at the level of design specifications set forth in NFPA 1901.
NFPA 1901 specifies that fire department pumpers must be
able to achieve three pressure/flow combinations. These are
100 percent of rated capacity at 150 psi (1034 kPa) net pump
pressure, 70 percent of rated capacity at 200 psi (1379 kPa) net
pump pressure, and 50 percent of rated capacity at 250 psi
(1724 kPa) net pump pressure. Therefore, a 1000 gpm
(3785 L/min) pumper can be expected to deliver no less than
1000 gpm (3785 L/min) at 150 psi (1034 kPa), 700 gpm
(2650 L/min) at 200 psi (1379 kPa), and 500 gpm (1893 L/
min) at 250 psi (1724 kPa). Residual supply pressure on the
suction side of a pump from a municipal or other pressurized
water supply can also be added. The 150 psi (1034 kPa) suggested
pressure is also found in NFPA 13E. It also states that this is
the pressure to be provided unless the sign at the fire department
connection states otherwise. It is not the intent of this
standard to limit the maximum pumper pressure at the fire
department connection inlet for manual or automatic standpipes
to 150 psi (1034 kPa).

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

<image003.jpg>

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, November 17, 2017 3:07 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: FDC sizing on wet automatic standpipes

Yeah, what Travis said.   Everyone should remember that FDC configurations and 
sizing take into account the chance that there may be obstruction or damage to 
an inlet, so providing four is not based on hydraulics only.    As for the pipe 
sizing … I have less energy about that and if it calc’s then it should be 
adequate.   But (and as per my usual rap)...

IT’S UP TO THE AHJ.

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Friday, November 17, 2017 12:03 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: FDC sizing on wet automatic standpipes

I don’t believe it matters what the building serves.  It is an automatic 
standpipe.  I don’t see in Chapter 7 of NFPA 14 2013 that says the FDC inlet 
shall be based on 250 gpm per inlet only if it is a manual standpipe.  I don’t 
see where you have to calculate through the FDC.  You may be able to use 4”, 
but you will still need 4 inlets.  I think that seems quite odd and would 
probably try to run it as 6” as a good practice.  However, I can’t see anything 
requiring the size of the piping to be any minimum.


<image005.jpg>
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, November 17, 2017 12:52 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: FDC sizing on wet automatic standpipes

Is this a residential or light hazard 8 story building?
Do you have a 1000 gpm fire pump from city water? Electric or diesel?
Reliable power with no outages?
3 - 4 or more standpipe risers?

Then you can get answers.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Friday, November 17, 2017 11:05 AM
To: 
[email protected]<mailto:[email protected]>
Subject: FDC sizing on wet automatic standpipes

I'm not lucky enough to be able to treat the FDC on a wet automatic standpipe 
as supplemental am I?
We have a building with a combined sprinkler and standpipe system that's wet 
automatic. Building is 8 stories, but separated. etc. etc.
Since the standpipe is wet automatic, the FDC isn't the only supply source, so 
do we still have to calculate it hydraulically? Total standpipe demand is 1000 
GPM
We're using NFPA 14, 2013 edition.
Basically, I'm trying to figure out if its OK to run 4" to the FDC and use a 
single Siamese instead of 6" piping to a 4-way or two Siamese connections.

Benjamin Young

<image006.jpg><https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>

Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to