Ben,

 

Sections 7.7.2, 7.12.3, and 7.12.3.1  should have the answers to your 
questions, but may not be the answers you’re looking for.

 

Ed

 

 

Ed Kramer

Bamford Fire Sprinkler Co., Inc.

5134 Merriam Dr./Shawnee Mission, KS  66203

Phone: 913-432-6688  Fax: 913-432-5294  Cell: 785-766-4894

[email protected]

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Friday, November 17, 2017 10:05 AM
To: [email protected]
Subject: FDC sizing on wet automatic standpipes

 

I'm not lucky enough to be able to treat the FDC on a wet automatic standpipe 
as supplemental am I?

We have a building with a combined sprinkler and standpipe system that's wet 
automatic. Building is 8 stories, but separated. etc. etc.

Since the standpipe is wet automatic, the FDC isn't the only supply source, so 
do we still have to calculate it hydraulically? Total standpipe demand is 1000 
GPM

We're using NFPA 14, 2013 edition.



Basically, I'm trying to figure out if its OK to run 4" to the FDC and use a 
single Siamese instead of 6" piping to a 4-way or two Siamese connections.



Benjamin Young