And 2 FDC’s within 150’ of hydrants for a high-rise?

Not to digress but I’m finding piping from FDC’s to feed mains not according to 
code more and more.  You’re not supposed to have any valves between the FDC and 
the Standpipes with only  Standpipe Isolation Valves being allowed.  

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, November 17, 2017 2:52 PM
To: [email protected]
Subject: RE: FDC sizing on wet automatic standpipes

 

Is this a residential or light hazard 8 story building?

Do you have a 1000 gpm fire pump from city water? Electric or diesel?

Reliable power with no outages?

3 - 4 or more standpipe risers?

 

Then you can get answers.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Friday, November 17, 2017 11:05 AM
To: [email protected]
Subject: FDC sizing on wet automatic standpipes

 

I'm not lucky enough to be able to treat the FDC on a wet automatic standpipe 
as supplemental am I?

We have a building with a combined sprinkler and standpipe system that's wet 
automatic. Building is 8 stories, but separated. etc. etc.

Since the standpipe is wet automatic, the FDC isn't the only supply source, so 
do we still have to calculate it hydraulically? Total standpipe demand is 1000 
GPM

We're using NFPA 14, 2013 edition.

Basically, I'm trying to figure out if its OK to run 4" to the FDC and use a 
single Siamese instead of 6" piping to a 4-way or two Siamese connections.



Benjamin Young

 


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
 

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
 www.avast.com 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to