Sure you have. They're called a lintel. They are commonly used to transition 
differing ceiling elevations between areas, or architecturally define spaces. 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Feb 16, 2018, at 3:31 PM, "[email protected]" 
> <[email protected]> wrote:
> 
> I never saw a wall that didn't go all the way down to the floor.
> Brad.
> Quoting "Mark.Phelps" <[email protected]>:
> 
>> So this minimum space rule applies to sprinklers under soffits and on either 
>> side of a lintel? I guess I have been of the understanding that this type of 
>> obstruction was effectively treated like a wall. Is that just not correct?
>> 
>> Mark at Aero
>> 602 820-7894
>> 
>> Sent from my iPhone
>> 
>> On Feb 16, 2018, at 2:23 PM, Roland Huggins 
>> <[email protected]<mailto:[email protected]>> wrote:
>> 
>> Reality can be cruel.  Without an approved variance, the very bad news is 
>> you have a noncomplying system and all the liability that goes with that.  
>> After all the crying and gnashing of teeth, sometimes mother has to pick a 
>> different baby.
>> 
>> Roland
>> 
>> 
>> 
>> Roland Huggins, PE - Senior VP Engineering
>> 
>> American Fire Sprinkler Assn.
>> 
>> Dallas, TX
>> 
>> http://secure-web.cisco.com/1wXO1nDy8iYAz2-wkUjZWf5n8JBJh5F1GYGMpa5sAkyrXcYp53UgWPDWk7yMm2GAuKGJs-SDyayG2YArmuwjrZSkbCU9sV2phXwIo5VxEdtibGkfHZUTyhybWoBEh0IsLyjXv912KxMOvIr6Bp4zH5R-GGaDYGo3LHJ9JrUeklb9Z5aYBcghFIysl62kH1aZTGXb8i7TgRoKKIgtxu4xmYvCUnboweqOpNXXl1Xcb9qO-9zgvOKDiRw6GUPr8MUhHd2RnanjOoBFe6hAWvVgxmg/http%3A%2F%2Fwww.firesprinkler.org<http://secure-web.cisco.com/1Rt5VGjvBwdQClxCl63sT3hzlyZTf89OCCrbNtgGCsO3On4Z4UYiPtZeyQZc3G8srveXMRaKYJxK379uyWN1rUNkwAFx_WYGZTWVDbKxKUjAoTDFl7M3G76LK-Mqf2PIiizG8QYGZt0haMrQ7hvgIJMe3kT5Y69SPu313KUYV1XKmyOmjQ8_u00Ujh5Vxeoa5ymesB1FeOOzKhrixOBGdCZqO5Wqi5o9FngecROu4osDq2W0vvxCXC1ZkYlpxPXuMK9VGDaPRZKUmSVCwDPyfSw/http%3A%2F%2Fwww.firesprinkler.org%2F>
>> 
>> 
>> Fire Sprinklers Saves Lives
>> 
>> 
>> 
>> 
>> On Feb 16, 2018, at 1:14 PM, Mark.Phelps 
>> <[email protected]<mailto:[email protected]>> wrote:
>> 
>> I the applications we work in (real buildings) it is not possible to do so. 
>> If I have a sprinkler 10 feet from an I Beam, I can only install the next 
>> sprinkler at the 8' minimum spacing from it. And if I space the first 
>> sprinkler at that same 8' from there, I am over spaced from the obstructing 
>> beam by 12". So...... what's a mother to do?
>> 
>> Mark at Aero
>> 602 820-7894
>> 
>> Sent from my iPhone
>> 
>> On Feb 16, 2018, at 12:16 PM, Roland Huggins 
>> <[email protected]<mailto:[email protected]>> wrote:
>> 
>> The one doesn’t negate the other. You have to comply with BOTH.
>> 
>> 
>> Roland Huggins, PE - Senior VP Engineering
>> American Fire Sprinkler Assn.
>> Dallas, TX
>> http://secure-web.cisco.com/11AaOLmB4GbEARu4YaU_u16EyUnzrX2BM5FR_tPL5oVcrPe8PDEMGFOFNTZw_W613QOFX-p1sOCSOHfzbYNg3lq2AMVYiobBQvuJWjxM0NYjqixKpqTKgio_t--XFyz30IGG9zBFtDRRS3mfB3wjC6Tpz07kT6wHABc6RZ35mypIW581pVqLhPpfXsddxen3NwS3TfOerPq1b_3AasUH9ODWU7WDUdHaicl5lQ0JD29Z9Vq_WHBRsimXtM3gnSFAH-lU-T0kssWfPvJKpNxzrNg/http%3A%2F%2Fwww.firesprinkler.org<http://secure-web.cisco.com/1hcpfq6Aet0_1h6nFu-avzR_O96qADNdz7alQIL6l8ARN5J1fl2qjc7_NrgAVKZTjFb_wSLnVCc-ii6BeuzcRj_5KiLISDVqFhq4U8P-fLL-5ZmSWaBpC97OW_8dtu0fucdeE1zC6HsmYX9T7p-VGpAqiAbDak32SQYIeclZQk_dLtQEXULnC7rXnByKRKhQ6EDKuoiJGtIcVjDttfCP9JvV8VOW3x7JJ9r8qxlt-QopgghPNDL9xalZgnxzPkD40_Ccz5ySp78CxMthuFOjNgQ/http%3A%2F%2Fwww.firesprinkler.org%2F>
>> 
>> Fire Sprinklers Saves Lives
>> 
>> 
>> 
>> 
>> On Feb 16, 2018, at 10:43 AM, Mark.Phelps 
>> <[email protected]<mailto:[email protected]>> wrote:
>> 
>> I'm away from the standards but doesn't NFPA 13 have a paragraph which 
>> addresses sprinkler spacing on both sides of an obstruction, and only limits 
>> the spacing to 1/2 the Maximum spacing from the obstruction? We routinely 
>> space ESFR/Storage sprinklers at 2'-0" from an I Beam on both sides in this 
>> application.
>> 
>> Mark at Aero
>> 602 820-7894
>> 
>> Sent from my iPad
>> 
>> On Feb 16, 2018, at 8:17 AM, Roland Huggins 
>> <[email protected]<mailto:[email protected]>> wrote:
>> 
>> You still need to get approval of the AHJ (as an equivalency) since NFPA 13 
>> does not allow it.
>> 
>> 
>> Roland Huggins, PE - Senior VP Engineering
>> American Fire Sprinkler Assn.
>> Dallas, TX
>> http://secure-web.cisco.com/1itLE6KI-0YvJ1O45X-H49Sz3FDbGxbyzHLZJkAbQXBXC6TUcVFrJZya7TLnA8Ut2OGf3AF_WbKtBmNFbDz5s0noy3S3-pWB0AzUSHu5TX6l1iqlQ05nFibAMML6rSjHcP5pmA8hp_QEbruyQaw8a1pTisuJwPbnzqdKMm7-YmBzD5DJlCkcneBQU0PxOeYljUgXfjbADGEM2pBaTCy610TUk2w7i3H2Pon6RScLsPAmSurc0ob7fCWUadpxLLUhMON7FFAP3xAa9PtY3ru4JdA/http%3A%2F%2Fwww.firesprinkler.org<http://secure-web.cisco.com/1gaQcMS-LbBp6Jj0YkGnzaHbPgLw41B9RPOI0VnW-c4TnRlVE5BDuXcfPtCJSlaixPN6oazrltd-gVfYKy5SIxjOXx3fGK-oJSgIZLjt2v_4tLTSl_zo-j4QUMb5xMJ1YCuEk-EDcY9PmTaVDXFfgyVdcNKIiV2tIPQHWo2OwgTWlgKRwc1qUlntQZ8jLjbkzoziLbfls6V43gltorbCDzFWQpfYoZaVpt2S6t3ARnRVM2N2Z4_x6xhXoSTzqRUEcnPQDA1t7pLPq2JKPI2a4Dw/http%3A%2F%2Fwww.firesprinkler.org%2F>
>> 
>> Fire Sprinklers Saves Lives
>> 
>> 
>> 
>> 
>> On Feb 16, 2018, at 6:45 AM, Brian Harris 
>> <[email protected]<mailto:[email protected]>> wrote:
>> 
>> Mark-
>> I got a phone call yesterday from a member of one of the committees who 
>> essentially said the same thing. I’ve re-spotted heads using ESFR in each 
>> pocket over the storage area and the calc’s are much better, still need to 
>> find some more cushion somewhere. Thanks again for the response.
>> 
>> Brian Harris, CET
>> BVS Systems Inc.
>> bvssytemsinc.com<http://secure-web.cisco.com/1FryT8Ikt3abUxObRrFIcU1_D5fdxxXawMJ3tRKAfDq1J4Bd5c3vb-ShiqIJ8cGUDkiq3_V7q046N6dQxTczruYMhD-lEpL1RhsWsaUFmYiqd3gBAEDa83CTrk--G9JndlyaOCQe3dmpbjAdUj0jN3tPRT5buhY8S44akmM4ZMmIyL6HGTRFVbMYdEP86VQa3NQsutibokLpiUk8O_Vhsc9q_gQqXMPItQerUZAn-QBFHtIKTkSIsrNDN4gPZcJfxuMwyvT327bVKTF0C6_TjZg/http%3A%2F%2Fbvssystemsinc.com%2F>
>> 
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Mark Sornsin [FAR]
>> Sent: Friday, February 16, 2018 9:41 AM
>> To: 
>> '[email protected]<mailto:[email protected]>'
>> Subject: RE: ESFR Heads in Concrete Tee's
>> 
>> This may not be an FM job – and FM doesn’t use the term ESFR anymore, but…
>> 
>> I am familiar with an FM job where storage (aka ESFR) sprinklers were used 
>> in every tee space of concrete tee construction – they were 30” deep tees. 
>> The rule against not spacing sprinklers closer than 8’ didn’t apply because 
>> the tees prevented cold soldering. The trick however is that FM has a 
>> minimum design area for their storage sprinkler calculations (Despite the 
>> base design being 12 sprinklers at a given pressure).  That area is 12 x the 
>> minimum sprinkler coverage area of 64 sq.ft., which is 768 sq.ft.
>> 
>> I.e. if your design area does not meet 768 sq.ft. FM requires you add 
>> sprinklers until you reach that threshold.
>> 
>> Again, the main point here is that the minimum spacing is meant for adjacent 
>> sprinklers, but not those obstructed from each other by construction 
>> features – at least in FM’s opinion.
>> 
>> 
>> <image002.jpg><http://secure-web.cisco.com/1naImZp36tbKvd-rE8Lq8Snmcp7AWVf_fow06qFuTm-3st78J7fiMwAVI_bZSfKbV6wmJdiNzVSMbwNLV028ySp6raYqy_Q2K2JVTnd0ZxsgYtz5q506xFQ_bhk1jibQFb6aQvvB88bxuhPNCNC0kFCKn7xOUgfe6J2znCw1bl_h4CmKWZLcDWLm6JX21oZmK9j6WUPti0yxNZ6lNsTXlHz2COB2_gK4L3Lf2eC7AGriuTv7dZAXZivw6En1vvQZ0teCMEC--V7PoruPz9p5DXA/http%3A%2F%2Fwww.summitcous.com%2F>
>> 
>> Mark Sornsin
>> Sr. Fire Protection Engineer
>> Direct: 701-499-1391
>> Cell: 701-526-8585
>> 
>> 
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Brian Harris
>> Sent: Thursday, February 15, 2018 3:29 PM
>> To: 
>> [email protected]<mailto:[email protected]>
>> Subject: ESFR Heads in Concrete Tee's
>> 
>> Looking for some confirmation that ESFR heads cannot be used with concrete 
>> tee construction when the tee is 26” deep. Cut sheet says in this case you’d 
>> have to put them in each bay but also says heads can’t be closer than 8’, 
>> tee’s are 6’ on center.
>> 
>> Brian Harris, CET
>> BVS Systems Inc.
>> Design Manager
>> bvssystemsinc.com<http://secure-web.cisco.com/1FryT8Ikt3abUxObRrFIcU1_D5fdxxXawMJ3tRKAfDq1J4Bd5c3vb-ShiqIJ8cGUDkiq3_V7q046N6dQxTczruYMhD-lEpL1RhsWsaUFmYiqd3gBAEDa83CTrk--G9JndlyaOCQe3dmpbjAdUj0jN3tPRT5buhY8S44akmM4ZMmIyL6HGTRFVbMYdEP86VQa3NQsutibokLpiUk8O_Vhsc9q_gQqXMPItQerUZAn-QBFHtIKTkSIsrNDN4gPZcJfxuMwyvT327bVKTF0C6_TjZg/http%3A%2F%2Fbvssystemsinc.com%2F>
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>> 
>> 
>> ______________________________________________________________________
>> This email has been scanned by the Symantec Email Security.cloud service.
>> For more information please visit 
>> http://www.symanteccloud.com<http://www.symanteccloud.com/>
>> ______________________________________________________________________
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://secure-web.cisco.com/1v29pH_Pv12MCVIYZWcII03d9rh18vJkqKynWqIjkkq7DbLzqzgeB60zUGoKUEFjFA1HZI1x-6xE3gK84UNL-nlidVpv9AYfFrwrV05NtincJoVvOg2kHirlwzZcXJrOP0YxPFeutnaGM5DHKh34-bWrtd3x__brgLoGabf4fiK-RgCPasZdwP5S2oS_tQgvM9RjMfl-UtLbnrhKTi49SCmTen1JtPFC1XtBTsG9II7NYHJAoITY4-lV_I_Ah3Q5I1X5AlG43DT7jj5MD2OVFow/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://secure-web.cisco.com/1v29pH_Pv12MCVIYZWcII03d9rh18vJkqKynWqIjkkq7DbLzqzgeB60zUGoKUEFjFA1HZI1x-6xE3gK84UNL-nlidVpv9AYfFrwrV05NtincJoVvOg2kHirlwzZcXJrOP0YxPFeutnaGM5DHKh34-bWrtd3x__brgLoGabf4fiK-RgCPasZdwP5S2oS_tQgvM9RjMfl-UtLbnrhKTi49SCmTen1JtPFC1XtBTsG9II7NYHJAoITY4-lV_I_Ah3Q5I1X5AlG43DT7jj5MD2OVFow/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://secure-web.cisco.com/1grPcJ4mL0wg7Ugy1MtPVege2glp9Q9PEjJIe5-4b2AeP5FtQ8tzBIj94mFeMVW6DL-8L_SaP5seLJu_Bwxfyyw1N913Qxiig7b5Eo9EBKmMMmIAJqb7BYn8Y0-HELryh4T6eosDwv6QL0UtsbJ1DG9dXWM7hqooKy8XuyCM7kAHbeA6BsKsaux5z95wueAXtX6es2U5OB0MAhnkEEJWVmmkdQeQee-rFQMMqKBt8e-i7s6BZNKA50JEQ1QWIsBqYYRB7PSxhA4VBB0Llru7CRw/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://secure-web.cisco.com/1grPcJ4mL0wg7Ugy1MtPVege2glp9Q9PEjJIe5-4b2AeP5FtQ8tzBIj94mFeMVW6DL-8L_SaP5seLJu_Bwxfyyw1N913Qxiig7b5Eo9EBKmMMmIAJqb7BYn8Y0-HELryh4T6eosDwv6QL0UtsbJ1DG9dXWM7hqooKy8XuyCM7kAHbeA6BsKsaux5z95wueAXtX6es2U5OB0MAhnkEEJWVmmkdQeQee-rFQMMqKBt8e-i7s6BZNKA50JEQ1QWIsBqYYRB7PSxhA4VBB0Llru7CRw/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://secure-web.cisco.com/1MGKAUyOTbzrEG5cBgLbPTrwzVyIY3WtJWQGkCtBliPmG1saz6cmmmqSa4wb4NJfPnthORyCMnZAZWHS8hBhZInXYvCg0KL0Oz7rmIwP0rTf0PiJeNuk5UehxTfctzmyOiYAjqGM1mRRGM6AM9LCFJkTkbpZtydhgbT6qCOPIXISM2gJ6XFeAkMMdfmtsCS-EYg9cRpBrOt2pn5LQNIP8JQ29ZrZj5g4azvPOFuHva8dPX2lre7ZQhTdyW9X63NHj9bqU0_uBj7gMAslI79md2g/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://secure-web.cisco.com/1MGKAUyOTbzrEG5cBgLbPTrwzVyIY3WtJWQGkCtBliPmG1saz6cmmmqSa4wb4NJfPnthORyCMnZAZWHS8hBhZInXYvCg0KL0Oz7rmIwP0rTf0PiJeNuk5UehxTfctzmyOiYAjqGM1mRRGM6AM9LCFJkTkbpZtydhgbT6qCOPIXISM2gJ6XFeAkMMdfmtsCS-EYg9cRpBrOt2pn5LQNIP8JQ29ZrZj5g4azvPOFuHva8dPX2lre7ZQhTdyW9X63NHj9bqU0_uBj7gMAslI79md2g/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://secure-web.cisco.com/1CE3_CIShlql4N95vaysnj8Y78sVtF8fMznA4qi3aocgInORQw0lDaZh9RGrEL3ZuEjpfj5pZcmhbz0jH6iOPsglDJ4I9xWHghNPicpj2BL94B4Y4R0tzqBNlY6hDxlvp4IDfzxIEKFmfwWAiAaKG8PgeMXA_TPqIBDUNEfqIvOtLctBPV-IHeYnWGxQWVTROjk6gSdGnd-2ZiMK35waLEJE8dYEgCtLVGwMHWq9rbfDfMLBBALU4SdN2U3uKHRPH/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to