I always try to contact the FM reviewer and ask for the table where they are 
getting the info in their datasheets.  I then put that table on the drawings so 
there is no question as to where the criteria was derived.

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

From: Sprinklerforum <[email protected]> On Behalf 
Of Brian Harris
Sent: Monday, June 4, 2018 8:55 AM
To: [email protected]
Subject: RE: FM Mutual & ESFR Heads

 

Mark-

So riddle me this, I’m working on a project that specifies ESFR heads and FM 
wants .42/2000. What are my options ?

 

Brian Harris, CET

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/> 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Sornsin [FAR]
Sent: Monday, June 04, 2018 11:46 AM
To: '[email protected]'
Subject: RE: FM Mutual & ESFR Heads

 

So the answer is, no. FM has not banned ESFR systems.  

 

They have just stopped recognizing the ESFR term.  Many sprinklers you know as 
‘ESFR’ they simply refer to as a ‘storage sprinkler.’  Likewise as Travis and 
Craig noted, there are some sprinklers they recognize as ‘storage’ that are not 
identified as ESFR by the manufacturer.

 

 


 <http://www.SummitCoUS.com> 

Mark Sornsin  
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Monday, June 04, 2018 9:26 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: FM Mutual & ESFR Heads

 

I may be having a senior moment but I swear I remember reading something about 
FM not allowing ESFR systems….. Is that even remotely true?

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to