If you have the info on the building, height , storage commodity and height use 
chapter 16 table 16.2.3.1 and it will tell you which ESFR and pressure.

Richard M. Carr
Project Manager/Design
Diboco Fire Sprinklers, Inc.
325 Jackson Loop Road
Flat Rock, NC  28731

rich...@diboco.com<mailto:rich...@diboco.com>
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile

[cid:image001.jpg@01D2E695.9A38B950]

[cid:image002.png@01D2E695.9A38B950]


From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Brian Harris
Sent: Monday, June 04, 2018 12:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FM Mutual & ESFR Heads

Richard-
But what pressure are you running the heads at?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Carr
Sent: Monday, June 04, 2018 11:59 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: FM Mutual & ESFR Heads

Because ESFR would exceed the density requirement, I would think FM would be 
happy if you used ESFR.

Richard M. Carr
Project Manager/Design
Diboco Fire Sprinklers, Inc.
325 Jackson Loop Road
Flat Rock, NC  28731

rich...@diboco.com<mailto:rich...@diboco.com>
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile

[cid:image001.jpg@01D2E695.9A38B950]

[cid:image002.png@01D2E695.9A38B950]


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Brian Harris
Sent: Monday, June 04, 2018 11:55 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: FM Mutual & ESFR Heads

Mark-
So riddle me this, I’m working on a project that specifies ESFR heads and FM 
wants .42/2000. What are my options ?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark Sornsin [FAR]
Sent: Monday, June 04, 2018 11:46 AM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: FM Mutual & ESFR Heads

So the answer is, no. FM has not banned ESFR systems.

They have just stopped recognizing the ESFR term.  Many sprinklers you know as 
‘ESFR’ they simply refer to as a ‘storage sprinkler.’  Likewise as Travis and 
Craig noted, there are some sprinklers they recognize as ‘storage’ that are not 
identified as ESFR by the manufacturer.


[Visit our Website at www.SummitCoUS.com]<http://www.SummitCoUS.com>

Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Monday, June 04, 2018 9:26 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: FM Mutual & ESFR Heads

I may be having a senior moment but I swear I remember reading something about 
FM not allowing ESFR systems….. Is that even remotely true?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to