You can do both designs (density/area and end head pressure), we do it 
frequently to cover different risks within the same area. A sprinkler doesn’t 
know what it is! It is just a orifice/k factor with some pressure behind it. We 
would typically use smaller ‘storage’/ESFR heads and do one calculation for the 
CMDA design and another one for the storage design.

For example:

The VK500 is a UL approved ESFR sprinkler. It is FM approved as a quick 
response non-storage sprinkler and also FM approved as a quick response storage 
sprinkler.

It can be used in various types of designs.



But I agree, clarification is required.


Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 2  Mobile: +64 (0)21 433 488  Email: 
ni...@protechdesign.co.nz<mailto:ni...@protechdesign.co.nz>  Skype: 
nicky-marshall Web :www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

“I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody” Lily Tomlin

From: MFP Design, LLC <tm...@mfpdesign.com>
Sent: Tuesday, 5 June 2018 4:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FM Mutual & ESFR Heads

ESFR are not spray sprinklers and can not be interchanged to meet a 
density/area curve.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Nick Maneen
Sent: Monday, June 4, 2018 9:08 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: FM Mutual & ESFR Heads

K=Q/•P
K=42/•7
K=42/2.65
K=15.85

Use K14 sprinklers or K16.8 depending on what your water supply is.

Nick Maneen, SET
c 704.791.7789


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Monday, June 04, 2018 11:55 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: FM Mutual & ESFR Heads

Mark-
So riddle me this, I’m working on a project that specifies ESFR heads and FM 
wants .42/2000. What are my options ?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark Sornsin [FAR]
Sent: Monday, June 04, 2018 11:46 AM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: FM Mutual & ESFR Heads

So the answer is, no. FM has not banned ESFR systems.

They have just stopped recognizing the ESFR term.  Many sprinklers you know as 
‘ESFR’ they simply refer to as a ‘storage sprinkler.’  Likewise as Travis and 
Craig noted, there are some sprinklers they recognize as ‘storage’ that are not 
identified as ESFR by the manufacturer.


[Visit our Website at www.SummitCoUS.com]<http://www.SummitCoUS.com>

Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Monday, June 04, 2018 9:26 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: FM Mutual & ESFR Heads

I may be having a senior moment but I swear I remember reading something about 
FM not allowing ESFR systems….. Is that even remotely true?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to