No, it's all good after the pump discharge control valve. A.4.7.7.2
On Fri, Jul 13, 2018 at 3:03 PM, Dewayne Martinez < dmarti...@total-mechanical.com> wrote: > Is there anything that restricts the use of a PRV after the discharge > control valve on a fire pump? > > I have a ESFR storage building where I am designing to a “future” water > supply which is much higher than the existing water supply. > > The fire pump must satisfy both existing and future conditions and I > thought about leaving a space for a PRV to be installed downstream of the > pump discharge valve to account for the future higher pressures. > > Thanks, > > > > Dewayne Martinez > > Fire Protection Design Manager > > > > *TOTAL* *Mechanical* > > *Building* *Integrity* > > > W234 N2830 Paul Rd. > Pewaukee, WI 53072 > > dmarti...@total-mechanical.com > > Ph: 262-522-7110 > > Cell: 414-406-5208 > > http://www.total-mechanical.com/ > > > > [image: A close up of a sign Description generated with high confidence] > > > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >