Does the FDC line connect downstream of the PRV? Would the fire engine operator 
supply other than 150 psi to the FDC?

Best.

Bruce Verhei 

> On Jul 13, 2018, at 16:20, Tom Duross <tduro...@comcast.net> wrote:
> 
> You’ll have #14 issues, if relevant and depending on adopted version.
> I will say that in-series setup with bypasses in 2013 #14 is a real PITA to 
> set due to valve creep.
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Fire Design
> Sent: Friday, July 13, 2018 6:32 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: PRV after pump discharge control valve
>  
> No, it's all good after the pump discharge control valve.
> A.4.7.7.2 
>  
>  
> On Fri, Jul 13, 2018 at 3:03 PM, Dewayne Martinez 
> <dmarti...@total-mechanical.com> wrote:
> Is there anything that restricts the use of a PRV after the discharge control 
> valve on a fire pump?
> I have a ESFR storage building where I am designing to a “future” water 
> supply which is much higher than the existing water supply. 
> The fire pump must satisfy both existing and future conditions and I thought 
> about leaving a space for a PRV to be installed downstream of the pump 
> discharge valve to account for the future higher pressures.
> Thanks,
>  
> Dewayne Martinez
> Fire Protection Design Manager
>  
> TOTAL Mechanical
> Building Integrity
> 
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
> dmarti...@total-mechanical.com
> Ph:  262-522-7110
> Cell: 414-406-5208
> http://www.total-mechanical.com/ 
>           
> <image001.jpg>
>  
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
>  
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org