I fully agree with Steve.  These sprinklers, if in the remote area, need to be 
calculated.

John

Sent from my iPad

On Sep 21, 2018, at 12:19 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:

The math doesn’t add up – how would eliminating sprinklers for four 10’x10’ 
closets save 14 sprinklers in the DA?  Notwithstanding those metrics, these are 
not small clothes closets, they are repositories for people’s “stuff”.  You 
have a prevailing ordinary hazard with accessory miscellaneous storage for lack 
of a better classification.  I respectfully disagree that eliminating 
sprinklers is consistent with the intent of the reference section.   100 sq. 
ft. packed with camping gear and seasonal toys is a very different condition 
from an interior closet that might only be 15-25 sq. ft in area.

Steve Leyton

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Nick Maneen
Sent: Friday, September 21, 2018 9:05 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: ELIMINATION OF SPRINKLERS IN CLOSETS FOR HYDRAULIC CALCULATIONS

If you are using the full design area, that is what that provision is for.  I’m 
referring to 23.4.4.7.2 in the 2016 Edition of NFPA 13.

Nick Maneen, SET
c 704.791.7789


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Friday, September 21, 2018 11:48 AM
To: 
[email protected]<mailto:[email protected]>
Subject: ELIMINATION OF SPRINKLERS IN CLOSETS FOR HYDRAULIC CALCULATIONS


I have a 3 story living condo.

There are 4 units which each have an open parking garage under the 2nd floor. 
Along the back wall are 4 (10sqft ) closets.

The engineer is asking for a dry system designed to .15/1950.

Just want to know what everyone's thoughts are about not including the 
sprinklers in these closets. Using the provision 23.4.4.6.2

It would allow me to eliminate 14 sprinklers from my calculation area.

Regards

Troy
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to