Yeah, already acknowledged that.

That’s …  not a sprinkler-friendly design, is it?    Architects and developers 
always say, “We don’t need a fire protection consultant, we leave that to the 
installing contractor.”  How are these “closets” built?  Are they lockers (i.e. 
fixtures) or are they framed walls?    I’m still not seeing how you can leave 
them out but looking for an angle here …

Steve

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, September 21, 2018 1:43 PM
To: [email protected]
Subject: Re:ELIMINATION OF SPRINKLERS IN CLOSETS FOR HYDRAULIC CALCULATIONS

Did you read the original email. 10sqft. They are not 10x10. They are 2x5.

Sent from my Huawei Mobile


-------- Original Message --------
Subject: RE: ELIMINATION OF SPRINKLERS IN CLOSETS FOR HYDRAULIC CALCULATIONS
From: Steve Leyton
To: [email protected]
CC:


The math doesn’t add up – how would eliminating sprinklers for four 10’x10’ 
closets save 14 sprinklers in the DA?  Notwithstanding those metrics, these are 
not small clothes closets, they are repositories for people’s “stuff”.  You 
have a prevailing ordinary hazard with accessory miscellaneous storage for lack 
of a better classification.  I respectfully disagree that eliminating 
sprinklers is consistent with the intent of the reference section.   100 sq. 
ft. packed with camping gear and seasonal toys is a very different condition 
from an interior closet that might only be 15-25 sq. ft in area.

Steve Leyton

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Nick Maneen
Sent: Friday, September 21, 2018 9:05 AM
To: [email protected]
Subject: RE: ELIMINATION OF SPRINKLERS IN CLOSETS FOR HYDRAULIC CALCULATIONS

If you are using the full design area, that is what that provision is for.  I’m 
referring to 23.4.4.7.2 in the 2016 Edition of NFPA 13.

Nick Maneen, SET
c 704.791.7789


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Friday, September 21, 2018 11:48 AM
To: [email protected]
Subject: ELIMINATION OF SPRINKLERS IN CLOSETS FOR HYDRAULIC CALCULATIONS


I have a 3 story living condo.

There are 4 units which each have an open parking garage under the 2nd floor. 
Along the back wall are 4 (10sqft ) closets.

The engineer is asking for a dry system designed to .15/1950.

Just want to know what everyone's thoughts are about not including the 
sprinklers in these closets. Using the provision 23.4.4.6.2

It would allow me to eliminate 14 sprinklers from my calculation area.

Regards

Troy