Sounds more like Pick Modules than walkways between racks. How far above the 
floor is the walkway, and is than one level?

Mark at Aero
602 820-7894

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Wednesday, May 22, 2019 9:47 AM
To: [email protected]
Subject: RE: [EXTERNAL] RE: ESFR and Obstructions - Sizing

This doesn't really answer your question, but how big are these branch lines? 
I'm surprised to hear that a walkway (for humans, right?) wouldn't be able to 
support a 2-1/2" branch line.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Wednesday, May 22, 2019 9:16 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: ESFR and Obstructions - Sizing

On a follow up to this, is there still the provision to just calculate 2 
additional ESFR sprinklers under the obstruction in lieu of same size pipng?

I have a situation where the owner/engineer required ESFR at the roof deck - 
way overkill and not needed for 18' of Class I-III storage.  Now, they came in 
and added a bunch of walkways between the racks in an area.  So, we now have 
42" wide obstructions below the ESFR sprinklers.  So, I have to put sprinklers 
below these walkways.  I don't see how I can call them in-rack sprinklers which 
would allow me K8 or K11.2 as in-racks.  That is why I have ESFR below the 
obstructions.  Now, of course the walk ways were not designed to have the large 
ESFR branch line and main sizes supported below them.  So, I am looking at 
other ways to possible solve this problem created by others.

Am I missing something here?

Thanks again for all of the help.

[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=Dc3QBI1gV378QBzWYXVrbx51gSZf7MF6YvWXh3x-VUU&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=D1lg7HTENtseQzklTV1INI2MaH_TRck0EvVtLnSaPFQ&s=Rufh01dDsy_npek5wt4pWmioIfvkSfN_1z6I8MZmYsA&e=>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=GLiLtst2fRVmIqIK29vYF5bPmL6ppwO9J30JWn4emCI&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=2hh8PEF6PcfNC0kZ0lGrXPze9PVB4Dqai-7vS9AEmGA&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Rocci 3 Cetani
Sent: Wednesday, May 22, 2019 9:12 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: ESFR and Obstructions - Sizing

Left out a number 23.4.4.7.3.2

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


[email protected]<mailto:[email protected]>
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.norcalfire.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=NX8k_IwaVYEHbwEK2QQVYnKgngvlCPD5dn9JCdzC5B4&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Rocci 3 Cetani
Sent: Wednesday, May 22, 2019 9:10 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: ESFR and Obstructions - Sizing

23.4.4.7.3

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


[email protected]<mailto:[email protected]>
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.norcalfire.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=NX8k_IwaVYEHbwEK2QQVYnKgngvlCPD5dn9JCdzC5B4&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Wednesday, May 22, 2019 9:05 AM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR and Obstructions - Sizing

Can some one help me locate the section in NFPA 13 (2016 preferred) that 
indicates when you have obstructions below the ESFR sprinklers, you supply the 
sprinkler below the obstruction with pipe size the same as the branch line and 
you don't include the additional sprinklers in the calculations?

The old method was to calc two additional sprinklers below the obstruction.  
But I believe it has been replaced with the criteria I mentioned.

[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=Dc3QBI1gV378QBzWYXVrbx51gSZf7MF6YvWXh3x-VUU&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=6oQnLIuAcWswpN5cvKLsLbvMjR0y8Et_kq8FiUIi0pw&e=>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=GLiLtst2fRVmIqIK29vYF5bPmL6ppwO9J30JWn4emCI&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=5E42PaIlNJ9szsnz0digz21buNhxqi3SDmRA8MUfjYE&s=2hh8PEF6PcfNC0kZ0lGrXPze9PVB4Dqai-7vS9AEmGA&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to