Do you ignore the walls if rated when using area/density method or does the 
rating cause you to have to stay within the limits of the rated walls?



Thanks,



Cliff Whitfield, SET

President



Fire Design, Inc.

184 Comfort Place

Burnsville, NC 28714

Ph: 828-284-4772







From: Sprinklerforum <[email protected]> On Behalf 
Of Roland Huggins
Sent: Thursday, July 11, 2019 2:16 PM
To: [email protected]
Subject: Re: ESFR Calc's



Bullseye



We IGNORE walls unless rated and using the room design approach is the starting 
point



Roland







Roland Huggins, PE


Senior Vice President, Engineering & Technical Services


American Fire Sprinkler Association


p:

214-349-5965 ext121


w:

 <http://firesprinkler.org> firesprinkler.org


 <https://www.facebook.com/firesprinkler.org/>    
<https://twitter.com/afsa/status/1039528345367732224>    
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>   
 <https://www.instagram.com/firesprinklerorg/>

4 days. 1,500+ attendees.
AFSA38: Convention, Exhibition, & Apprentice Competition is North America's 
largest fire sprinkler trade event. Join us at the Manchester Grand Hyatt in 
beautiful San Diego, California October 1-4, 2019.





On Jul 10, 2019, at 10:17 AM, Sean.VanGaal <[email protected] 
<mailto:[email protected]> > wrote:



Do what Mike said but pick up the 12th sprinkler off the 4th line.  I would 
imagine the intent of NFPA 13 was to calculated 4 sprinklers on a line as your 
worst case scenario to prove the line size.  Then pickup 12 sprinklers total to 
get an appropriate total flow.  So the standard reference 3 lines to do this as 
that is the common scenario.



Applying this assumption to your scenario, your 1st two lines have at least 4 
sprinklers per line so those are easy enough.  Your 3rd line only has 3 
sprinklers so pickup all 3 and then pick up the 4th sprinkler on the 4th line.  
You now have 12 total sprinklers flowing, and the last 4 of these sprinklers 
are going to overflow more than they normally would if they were on a single 
line (assuming tree/end fed system).  So this should be a more conservative 
design than what NFPA 13 requires.  But you also aren’t forcing yourself to go 
ultra conservative by calculating 5 or 6 sprinklers on a single line which I do 
not believe was NFPA 13’s intent.



Thanks,

Sean VG



From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, July 9, 2019 7:44 AM
To:  <mailto:[email protected]> 
[email protected]
Subject: [EXTERNAL] RE: ESFR Calc's



Mike-

The lines on the other side of the wall only have (3) heads per line.



Brian Harris, CET

BVS Systems Inc.

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=AWdzKMSnfZTO1yzpl1Dd37Lrr1TeI1Fqx3BWjEHd-Zg&s=QGuUWxAksuh7c7L6oHoglZLzKjOOXn6OYIs8o4Fgsv4&e=>
 bvssytemsinc.com



From: Sprinklerforum < <mailto:[email protected]> 
[email protected]> On Behalf Of Mike Hairfield
Sent: Tuesday, July 09, 2019 10:36 AM
To:  <mailto:[email protected]> 
[email protected]
Subject: Re: ESFR Calc's



Why don't you use 2 lines on one side of the wall and 1 line on the other side 
of the wall thus 3 lines with 4 heads?



Mike



  _____

From: Sprinklerforum < <mailto:[email protected]> 
[email protected]> on behalf of Brian Harris < 
<mailto:[email protected]> [email protected]>
Sent: Tuesday, July 9, 2019 10:29 AM
To:  <mailto:[email protected]> 
[email protected]
Subject: ESFR Calc's



I have an ESFR system that I do not have (3) rows of (4) heads to calc. Due to 
compartment wall layouts I have (2) rows of (6) heads and (6) rows of (3) 
heads. What is the best way to grab (12) heads?



Brian Harris, CET

BVS Systems Inc.

Design Manager

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=AWdzKMSnfZTO1yzpl1Dd37Lrr1TeI1Fqx3BWjEHd-Zg&s=QGuUWxAksuh7c7L6oHoglZLzKjOOXn6OYIs8o4Fgsv4&e=>
 bvssystemsinc.com

Phone: 704.896.9989

Fax: 704.896.1935



_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]> 
[email protected]
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to