The standard recognizes EC is okay.  The standard recognizes the hazard can be 
treated as light in the standard spray section.  I would assume this was just 
missed or overlooked with regards to the EC section when they added the “light 
hazard” part to the standard spray section.

My opinion is this should be treated as LH but since you don’t have concrete 
evidence in the book pointing to a Light hazard EC sidewall you should have a 
conversation with the AHJ.  Personally I think it unnecessary to have an 11.2K 
sprinkler required at this location for the extremely slim chance of a fire 
starting under and open garage door.  Further, you said it is an OH building, 
you are just looking to control a fire from spreading, not suppressing the 
fire.  If the 8K EC sidewall can’t control a fire under your 16x14 door long 
enough for the fire department to show up, you still have all those other 
sprinklers around the door to help out.  With oodles and oodles of safety 
margin at every step of the way to get to your final design.  Again, this is my 
opinion and it all comes down to the person on the other side of table if they 
agree or not.

I actually submitted a public input on this very topic for the 2022 edition to 
try to get LH added to the EC section because we have run across this a few 
times.  Fingers crossed it goes through!

Thanks,
Sean VG

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Friday, August 23, 2019 2:26 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack <tm...@mfpdesign.com>
Subject: [EXTERNAL] Re: Ex cov under OH Door

I agree that the ex cov sprinklers can be used. But do you need one listed for 
Ordinary Hazard or can you use one listed for light hazard.

Spray sprinklers specifically say light is acceptable. Ex cov doesn’t say light 
is acceptable.

Question comes from an owner question. They have OH doors that are 16x14. 
Current design is 1 spray sprinkler on each side because 14’ max spacing. Owner 
wants 1 sprinkler. Question is just if can use ex cov sidewall listed for light 
or do they need to go OH listing.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=dp-F-j0Oj6rv0xnKAAFGmoMbAorL4SysGvxbvtLaW50&s=nzNTsluU3hgr62iPmEDNrbrwBPO3dtLJLqmSudGDqkA&e=>

Sent from my iPhone

On Aug 23, 2019, at 2:21 PM, Mike Stossel via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to protect 
areas below a single overhead door(s)

Mike Stossel SET
<image002.png>
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Friday, August 23, 2019 5:13 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack <tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>>
Subject: Ex cov under OH Door

Question has been brought up. Can you use ex cov sidewall listed for light 
hazard under overhead door in an ordinary hazard building?

I was under the impression it was not an issue. There is wording in section on 
standard spray sidewall that you can. But the same wording is not in the 
section under ex cov sidewall sprinklers. Since location has meaning, it made 
me question.



Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign-2Ccom&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=dp-F-j0Oj6rv0xnKAAFGmoMbAorL4SysGvxbvtLaW50&s=Tr1wAIcqWOE6s_N4lNsQ92iyf4y3hQfrOvzkhzpvi_M&e=>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=dp-F-j0Oj6rv0xnKAAFGmoMbAorL4SysGvxbvtLaW50&s=nzNTsluU3hgr62iPmEDNrbrwBPO3dtLJLqmSudGDqkA&e=>

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=XSIweKhAHHhyB-d63TCLaTQ55VHpbhIhFOxEPFjbNpg&m=dp-F-j0Oj6rv0xnKAAFGmoMbAorL4SysGvxbvtLaW50&s=75cYxLAErPhCoB7iE4o824ZRt23EFAdVRjn470xNbSc&e=>