Comment from past AHJ: For a couple heads, I doubt my field inspectors would 
notice difference. Either is going to operate the water flow switch, and get 
some water on the fire. I can’t see fire spreading laterally. First head should 
not cause problems with first four or six heads flow at ceiling.

Move on to bigger fish.

Best.

Bruce Verhei 

> On Aug 23, 2019, at 15:31, Travis Mack via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I agree with everything. This wasnt even my project. Was helping out a 
> customer of a colleague. 
> 
> My initial reaction was of course a single EC sidewall for LH is acceptable. 
> The installing contractor was pushing back saying you couldn’t do an EC HSW 
> for light hazard under the door. That was when I started to dig further and 
> noticed the missing wording in EC HSW. 
> 
> Installer was pushing back an ECOH HSW would cause the overhead to over 
> discharge and no longer work. I suggested to stop spending so much time and 
> $$ on this. Go with the ECOH HSW and pipe with same size as overhead branch 
> piping. That way there can be no push back. 
> 
> Just another fun Friday at the office. 
> 
> Travis Mack, CFPS, CWBSP, RME-G, SET
> 480-505-9271
> MFP Design, LLC
> www.mfpdesign,com
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> 
>> On Aug 23, 2019, at 3:25 PM, Sean.VanGaal via Sprinklerforum 
>> <sprinklerforum@lists.firesprinkler.org> wrote:
>> 
>> The standard recognizes EC is okay.  The standard recognizes the hazard can 
>> be treated as light in the standard spray section.  I would assume this was 
>> just missed or overlooked with regards to the EC section when they added the 
>> “light hazard” part to the standard spray section.
>>  
>> My opinion is this should be treated as LH but since you don’t have concrete 
>> evidence in the book pointing to a Light hazard EC sidewall you should have 
>> a conversation with the AHJ.  Personally I think it unnecessary to have an 
>> 11.2K sprinkler required at this location for the extremely slim chance of a 
>> fire starting under and open garage door.  Further, you said it is an OH 
>> building, you are just looking to control a fire from spreading, not 
>> suppressing the fire.  If the 8K EC sidewall can’t control a fire under your 
>> 16x14 door long enough for the fire department to show up, you still have 
>> all those other sprinklers around the door to help out.  With oodles and 
>> oodles of safety margin at every step of the way to get to your final 
>> design.  Again, this is my opinion and it all comes down to the person on 
>> the other side of table if they agree or not.
>>  
>> I actually submitted a public input on this very topic for the 2022 edition 
>> to try to get LH added to the EC section because we have run across this a 
>> few times.  Fingers crossed it goes through!
>>  
>> Thanks,
>> Sean VG
>>  
>> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
>> On Behalf Of Travis Mack via Sprinklerforum
>> Sent: Friday, August 23, 2019 2:26 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: Travis Mack <tm...@mfpdesign.com>
>> Subject: [EXTERNAL] Re: Ex cov under OH Door
>>  
>> I agree that the ex cov sprinklers can be used. But do you need one listed 
>> for Ordinary Hazard or can you use one listed for light hazard. 
>>  
>> Spray sprinklers specifically say light is acceptable. Ex cov doesn’t say 
>> light is acceptable. 
>>  
>> Question comes from an owner question. They have OH doors that are 16x14. 
>> Current design is 1 spray sprinkler on each side because 14’ max spacing. 
>> Owner wants 1 sprinkler. Question is just if can use ex cov sidewall listed 
>> for light or do they need to go OH listing. 
>> 
>> Travis Mack, CFPS, CWBSP, RME-G, SET
>> 480-505-9271
>> MFP Design, LLC
>> www.mfpdesign,com
>> Send large files to MFP Design via:
>> https://www.hightail.com/u/MFPDesign
>>  
>> Sent from my iPhone
>> 
>> On Aug 23, 2019, at 2:21 PM, Mike Stossel via Sprinklerforum 
>> <sprinklerforum@lists.firesprinkler.org> wrote:
>> 
>> NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to 
>> protect areas below a single overhead door(s)
>>  
>> Mike Stossel SET
>> <image002.png>
>> 36 Barren Road
>> East Stroudsburg, PA 18302
>> Office: 973-670-2627
>> m...@knssprinkler.com
>>  
>> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On 
>> Behalf Of Travis Mack via Sprinklerforum
>> Sent: Friday, August 23, 2019 5:13 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: Travis Mack <tm...@mfpdesign.com>
>> Subject: Ex cov under OH Door
>>  
>> Question has been brought up. Can you use ex cov sidewall listed for light 
>> hazard under overhead door in an ordinary hazard building?
>>  
>> I was under the impression it was not an issue. There is wording in section 
>> on standard spray sidewall that you can. But the same wording is not in the 
>> section under ex cov sidewall sprinklers. Since location has meaning, it 
>> made me question. 
>>  
>>  
>>  
>> Travis Mack, CFPS, CWBSP, RME-G, SET
>> 480-505-9271
>> MFP Design, LLC
>> www.mfpdesign,com
>> Send large files to MFP Design via:
>> https://www.hightail.com/u/MFPDesign
>>  
>> Sent from my iPhone
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org