In my opinion, no.  The flexible drop assembly is anchored to the ceiling.
The point of this requirement is to keep the pendent sprinkler from moving
upwards during activation.  The flexible drop assembly accomplishes this
requirement.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Help AFSA “Sound the Alarm” about sprinklers!*

AFSA’s charitable partner the American Red Cross is educating millions
through its Home Fire Preparedness Campaign. Help us support the inclusion
of fire sprinklers in their messaging.  Donate today!
<https://www.redcross.org/donate/cm/afsa-pub.html/>


On Fri, May 29, 2020 at 11:28 AM Dewayne Martinez via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Is the hanger on the pipe supplying a flexible drop to a pendant sprinkler
> in a ceiling still required to one that prevents upward movement?
>
> Sections 9.2.3.4.4.1,9.2.3.5.2.2
>
>
>
> Thank you,
>
>
>
> Dewayne Martinez
>
> Fire Protection Design Manager
>
>
>
> *TOTAL Mechanical*
>
> *Building* *Integrity*
>
>
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
>
> dmarti...@total-mechanical.com
>
> Ph:  262-522-7110
>
> Cell: 414-406-5208
>
> http://www.total-mechanical.com/
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to