Thanks everyone for the input.  My fitter brought this up to me and after I
read the sections I was still not sure.  John’s comment makes perfect
sense.



Thank you,



Dewayne Martinez

Fire Protection Design Manager



*TOTAL* *Mechanical*

*Building* *Integrity*


W234 N2830 Paul Rd.
Pewaukee, WI  53072

dmarti...@total-mechanical.com

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/





*From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
Behalf Of *John Denhardt via Sprinklerforum
*Sent:* Friday, May 29, 2020 10:41 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* John Denhardt <jdenha...@firesprinkler.org>
*Subject:* Re: NFPA 13, 2013 ed - hangers and pressures above 100psi



In my opinion, no.  The flexible drop assembly is anchored to the ceiling.
The point of this requirement is to keep the pendent sprinkler from moving
upwards during activation.  The flexible drop assembly accomplishes this
requirement.



Thanks,

John



John August Denhardt, PE

*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*

m: p:

301-343-1457
214-349-5965 ext 121

w:

firesprinkler.org

<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Help AFSA “Sound the Alarm” about sprinklers!*

AFSA’s charitable partner the American Red Cross is educating millions
through its Home Fire Preparedness Campaign. Help us support the inclusion
of fire sprinklers in their messaging.  Donate today!
<https://www.redcross.org/donate/cm/afsa-pub.html/>





On Fri, May 29, 2020 at 11:28 AM Dewayne Martinez via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

Is the hanger on the pipe supplying a flexible drop to a pendant sprinkler
in a ceiling still required to one that prevents upward movement?

Sections 9.2.3.4.4.1,9.2.3.5.2.2



Thank you,



Dewayne Martinez

Fire Protection Design Manager



*TOTAL Mechanical*

*Building* *Integrity*


W234 N2830 Paul Rd.
Pewaukee, WI  53072

dmarti...@total-mechanical.com

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/





_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to