I think the rationale is that for a project in the downtown areas, your flow 
test is already accounting for those buildings being active.  In the new 
development, your flow test is not accounting for those since they don't yet 
exist. 

However, I am glad the commentary in the 13R handbook (2016) specifically 
states it is only to include one building when you have multiple on a site.  It 
would be great if that could make it in to the body of the standard.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
www.mfpdesign.com

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
 
LinkedIn: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://www.ferguson.com/account-registration to register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features. 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
 or 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Bob Knight via Sprinklerforum
Sent: Thursday, November 12, 2020 11:27 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight <b...@firebyknight.com>
Subject: RE: Domestic Demands 13R

"However, they may be expected to have domestic demands. That is the plan 
reviewer rationale in one particular case."
Does the reviewer apply this same logic when doing a project in a downtown area 
with hundreds of buildings all using water at the same time?
I would assume not. So, why would this be any different? The domestic demand 
needs to be added only when sharing the water supply from the same line for 
each individual building. This is not a collective requirement.



Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Thursday, November 12, 2020 9:53 AM
To: mailto:philli...@pyebarkerfire.com; 
mailto:sprinklerforum@lists.firesprinkler.org
Cc: mailto:travis.m...@mfpdesign.com
Subject: RE: Domestic Demands 13R

Correct. However, they may be expected to have domestic demands. That is the 
plan reviewer rationale in one particular case.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
http://www.mfpdesign.com

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
 
LinkedIn: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing? Build a material quote? Check 
availability ? Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://www.ferguson.com/account-registration to register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features. 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
 or 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**

From: Mark Phillips <mailto:philli...@pyebarkerfire.com> 
Sent: Thursday, November 12, 2020 9:51 AM
To: mailto:sprinklerforum@lists.firesprinkler.org; Travis Mack 
<mailto:travis.m...@mfpdesign.com>
Subject: Re: Domestic Demands 13R

From a practical perspective all of the apartment building would not be 
expected to be on fire at once.

That was how a plan reviewer once explained it to me.


Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections
Service, Backflows, Fire Alarm Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : http://www.pyebarkerfire.com

________________________________________
From: Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org> on 
behalf of Mark Phillips via Sprinklerforum 
<mailto:sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 12, 2020 11:46:23 AM
To: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>; 
mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Mark Phillips <mailto:philli...@pyebarkerfire.com>
Subject: Re: Domestic Demands 13R 

[EXTERNAL]

Sorry if I was not clear only the demand of the building or buildings that 
share the 4 inch supply .

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections
Service, Backflows, Fire Alarm Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : http://www.pyebarkerfire.com

________________________________
From: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
Sent: Thursday, November 12, 2020 11:44:10 AM
To: Mark Phillips <mailto:philli...@pyebarkerfire.com>; 
mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Domestic Demands 13R

[EXTERNAL]

So in this case, you would be adding a total demand of 2500 gpm (20 buildings 
at 125 gpm each) to your sprinkler calc? And yes, it would be included at the 
point of each 4” connection to the 8” main. Seems excessive, but I have seen it 
requested that way. I have more commonly done what Matt states to only include 
the building of interest in the calc.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
http://www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
LinkedIn: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing? Build a material quote? Check 
availability ? Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://www.ferguson.com/account-registration to register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features. 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
 or 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**

From: Mark Phillips <mailto:philli...@pyebarkerfire.com>
Sent: Thursday, November 12, 2020 9:41 AM
To: mailto:sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack <mailto:travis.m...@mfpdesign.com>
Subject: Re: Domestic Demands 13R

Assuming the 8 inch supply loops the complex
Add the domestic demand at the 4” point on the loop for each building

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections
Service, Backflows, Fire Alarm Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : mailto:philli...@pyebarkerfire.com
Web : http://www.pyebarkerfire.com

________________________________________
From: Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org> on 
behalf of Travis Mack via Sprinklerforum 
<mailto:sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 12, 2020 11:34:20 AM
To: mailto:sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: mailto:travis.m...@mfpdesign.com <mailto:travis.m...@mfpdesign.com>
Subject: Domestic Demands 13R

[EXTERNAL]

Forumites:

Per 13R 9.6 it requires the domestic demand for the building being calculated 
to be added to the fire sprinkler system. This is generally not an issue. If 
you have a complex of say 20 buildings on site that is supplied by a common 
water line serving both domestic and fire, are you required to include the 
domestic demand for each building on the site water main.

For example, if I have a project with a 8" main going through the complex, and 
4" lead-ins to each building, with a domestic demand of 125 gpm for each 
building, how are you doing the domestic demand? With the domestic / fire split 
in the building, it is required to include the 125 gpm demand in addition to 
the fire sprinkler system demand in the 4" line. Are you including the other 
2375 gpm (19 additional buildings at 125 gpm domestic allowance), in your 
calculations back to the city main?

This seems quite excessive. If it were a 13 system, you would have similar 
flows and a 100 gpm hose allowance. There is no requirement in this example to 
include the domestic in a 13 system. But, if you are required to include the 
additional 2375 gpm, that could be quite taxing on the site supply. Again, how 
is everyone handling it.

We have seen AHJ's take both approaches on this.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:travis.m...@mfpdesign.com
http://www.mfpdesign.com

Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing? Build a material quote? Check 
availability ? Searching for an invoice?
*If you do not already have an account with ferguson.com, click here to 
register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features. Apple iOS devices or Android devices**

_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to